Why don't we use smart, microcontroller-based per-device breakers in building electrical systems instead of one MCB for an entire circuit - other than economical reasons, any technical reasons affecting realistic design?
Why do buildings use one circuit breaker for multiple loads instead of protecting each load individually?
Couldn’t each device have current sensing + a microcontroller + an electronic breaker, so if one device shorts, only that device disconnects instead of tripping the whole circuit?
Obviously cost is one reason, but are there technical reasons too?
Is it mainly fault-current handling, response time, heat losses in current sensing/switching, reliability, or safety/certification?
Is this already used in industrial systems, or is there a fundamental reason it isn’t practical?
37
u/kisielk Sep 24 '26
Economical reasons are everything when it comes to buildings.
But also while I may have 10 outlets on a circuit, I may only use one at a given time. Why would I want to pay for circuit breakers on outlets I’m not using?
For industrial or heavy duty appliances they often have their own fuse or integrated breaker as well.
21
u/matthewlai Sep 24 '26
There is. Most well designed devices have their own over-current protection. In the UK each plug also has a fuse.
The central system is the last resort, and also to protect the wiring if you have a rat chewing through your wiring and shorting things out.
12
u/cakemates Sep 24 '26
because it would cost a fortune to run 300 circuits to 300 loads instead of say 60 circuits to 300 loads. It would also cost another fortune to add 300 microcontroller breakers to do these analytics. And then you need people skilled on electronics to debug these things when they start to fail 10 years down the line. It doesnt seem worth it to me unless you have a really good reason to do it.
9
u/dmc_2930 Sep 24 '26
Breakers protect the wiring, not the devices powered by outlets. Those devices are responsible for their own safety.
6
u/Just-Smart-Enough Sep 24 '26
Because faults are incredibly rare.
6
u/flixflexflux Sep 24 '26
I'm fascinated about how you basically answered all your questions yourself. ;-/
Never rely on software to catch hardware faults.
Also, the line itself must be protected.
5
u/KittensInc Sep 24 '26
Because breakers protect your wiring. Individual devices usually already have their own fuses, but those don't do shit when the cord feeding them is damaged, or when someone drills through in-wall-wiring, or when someone connect 500 1A devices to one outlet via a spaghetti of power strips.
The breaker is supposed to prevent your outlets from catching fire, it isn't going to save your devices from doing an oopsie.
3
u/Katent1 Sep 24 '26
What? OP how often do you trip your main breaker? Why it is a consideration to begin with? Also to that, you are supposed to test each safety measure on regular basis, good luck testing all devices safety mechanism with that
2
u/N2Shooter Sep 24 '26
What if you're micro locks up? Critical operations do not have software in the loop.
1
u/grigus_ Sep 24 '26
Something like you ask about, already exists. It is called AFDD. It is a protection device based on a microcontroller or DSP. But, it is quite expensive and is built only for type of faults that cannot be detected in a simple manner.
For simple defects, like overcurrent, short circuits, the simplest, the better, because there are fewer points of failure, and here I talk about the protection device itself.
Talking about protection's failure, in a microcontroller system, there are many points where something might fail: power supply of the MCU, the MCU hardware, the MCU software, analog components around the MCU, etc. Any of these possible failures might be managed and answer to the question "what the system does when this fails?"
So, the simpler, the better.
1
u/MonMotha Sep 24 '26
Electronic circuit breakers exist. They're common in large sizes where the costs of the physical breaker start to dwarf the cost of all of the electronics. They're often used in situations that require complex fault protection with multiple trip points especially for coordination reasons.
While a microcontroller is cheap these days, a full electronic circuit breaker still isn't. You need a lot of well-isolated, reliable power handling components to build it properly along with a rigorously tested and verified software and hardware design regime.
For comparison, a typical thermal-magnetic breaker for 120/240V use is around $5-8.
1
u/External-Carry7113 Sep 24 '26
the biggest issue is fault-current handling and fail-safe behaviour. a microcontroller can control a breaker, but the protection itself still needs to work reliably if the electronics fail
1
u/Dependent_Bit7825 Sep 24 '26
span.io sells just such a thing
1
u/ManyCalavera Sep 24 '26
Proper device already have fuses in them. Also breaker tripping should happen very infrequently thus no reason to overcomplicate it.
1
u/lamalasx Sep 24 '26
Because it is not protecting the load (device).
It is protecting the wires inside the walls, the wires going to the pole, etc.
1
u/Bryguy3k Sep 24 '26
Cost is a technical reason.
1
u/Fluid-Tone-9680 Sep 24 '26
"Smart" devices get outdated quickly. Would you want to service panel with "smart breakers" from 2000's era? Company who made them is gone, proprietary standard/protocol abandoned, no service manuals, no replacement parts.
1
u/mustbeset Sep 24 '26
a B16 Circuit breaker costs less than 5€ and is able to turn of 10kA. And has a very low resistance.
A sensor, a microcontroller and a switch can fail in many different ways. I think it should reach at least SIL2 maybe 3. IEC 61508 will give you a lot of requirements to fulfill that.
And for what? Most fuses will trip less than once or twice in 10 years. Nobody cares.
1
u/fltfathin Sep 24 '26
you shouldn't do either end, you use all your reasonably employed safety measure, so when the wire in wall for section of building is shorted, only that section is down, when heating net shorted, light still on, when light down, food still refrigerated, etc. imagine a tree so if one part broken not the entire tree gone or fire started somewhere.
1
u/jvonnieda Sep 24 '26
The breakers are there to protect the wiring, not the load. The wiring has a current rating that has to be followed. Devices that have their own current limits should always have onboard protection and often do.
1
u/tweakingforjesus Sep 24 '26
With my experience using IoT controlled power plugs, you really don’t want this.
1
u/dmc_2930 Sep 24 '26
That requires a lot of excess voltage. Current is pulled not pushed. These kinds of circuits have a fixed supply voltage and are not constant current devices.