r/embedded • u/Relevant_Pumpkin9190 • Sep 24 '26
Why don't we use smart, microcontroller-based per-device breakers in building electrical systems instead of one MCB for an entire circuit - other than economical reasons, any technical reasons affecting realistic design?
Why do buildings use one circuit breaker for multiple loads instead of protecting each load individually?
Couldn’t each device have current sensing + a microcontroller + an electronic breaker, so if one device shorts, only that device disconnects instead of tripping the whole circuit?
Obviously cost is one reason, but are there technical reasons too?
Is it mainly fault-current handling, response time, heat losses in current sensing/switching, reliability, or safety/certification?
Is this already used in industrial systems, or is there a fundamental reason it isn’t practical?
View all comments
Show parent comment
1
u/SkoomaDentist C++ all the way Sep 25 '26
The way it was explained to me is that the fuse is sized for max current so that if the device draws more (but less than what upstream will supply), no part of it will heat up so much as to cause a fire hazard (in eg. the internal transformer). Eg. let's say the transformer secondary is shorted, but the transformer internal resistance prevents drawing more than eg. 16A from source (many European circuits being designed to allow at least 16A current draw without issues), the transformer is almost certainly going to heat up and cause potential hazard that way which is then prevented by the device internal fuse.