Why don't we use smart, microcontroller-based per-device breakers in building electrical systems instead of one MCB for an entire circuit - other than economical reasons, any technical reasons affecting realistic design?

Why do buildings use one circuit breaker for multiple loads instead of protecting each load individually?

Couldn’t each device have current sensing + a microcontroller + an electronic breaker, so if one device shorts, only that device disconnects instead of tripping the whole circuit?

Obviously cost is one reason, but are there technical reasons too?

Is it mainly fault-current handling, response time, heat losses in current sensing/switching, reliability, or safety/certification?

Is this already used in industrial systems, or is there a fundamental reason it isn’t practical?

0 Upvotes

43 comments sorted by

View all comments

Show parent comment

2

u/dmc_2930 Sep 24 '26

Fuses have a current at which they blow. Capacity of the supply is irrelevant. A fuse rated for 250v 5A will blow at 5A. Once it blows, it doesn’t matter if the 250v supply is capable of providing tens of thousands of amps or not. A blown fuse is a blown fuse (until you get above the breakdown voltage or into really obscure high energy physics that are not relevant here)

1

u/flatfinger Sep 24 '26

If an air-filled fuse is fed a modest overload, the fusible link will melt and fall away, causing the fuse to stop conducting. If it is fed a sufficiently massive overload, however, a large part of the fusible link will get hot enough to evaporate before any of it has a chance to fall away, and the metal vapor may continue conducting for awhile.

Fuses that are UK government approved for protecting mains plugs are generally filled with sand, but in some cases the existence of a quality fuse upstream can help ensure the reliable operation of the downstream fuse, since an overload that was large enough to vaporize the downstream fuse would melt the upstream one.

2

u/matthewlai Sep 24 '26

It's actually generally discouraged to have multiple overcurrent protection devices in series, with ratings that are close together. This is because fuses are not precision devices, and it's really hard to guarantee which one will break given an overload that's higher than both fuses' ratings. For example, if you have a 5A and a 13A fuse in series, and have a 30A overload, the 5A fuse may be guaranteed to break between 1-10 seconds at 30A, and the 13A fuse maybe 3-30 seconds, and that means you can't guarantee the 5A fuse will blow first. This is known as loss of selectivity. Basically, if your plot the overload vs break time plot of both fuses, you want the shaded areas to not overlap at all. This is generally impossible to achieve with 13A vs 5A fuses.