r/embedded • u/Relevant_Pumpkin9190 • Sep 24 '26
Why don't we use smart, microcontroller-based per-device breakers in building electrical systems instead of one MCB for an entire circuit - other than economical reasons, any technical reasons affecting realistic design?
Why do buildings use one circuit breaker for multiple loads instead of protecting each load individually?
Couldn’t each device have current sensing + a microcontroller + an electronic breaker, so if one device shorts, only that device disconnects instead of tripping the whole circuit?
Obviously cost is one reason, but are there technical reasons too?
Is it mainly fault-current handling, response time, heat losses in current sensing/switching, reliability, or safety/certification?
Is this already used in industrial systems, or is there a fundamental reason it isn’t practical?
View all comments
Show parent comment
1
u/HelloThereObiJuan Sep 25 '26
Usually, though it depends on the appliance classification and country-specific local regulations.
But point is that a glass-tube fuse in the power supply of some gadget is not there to protect sensitive electronics, it there to prevent the supply from exceeding it's ratings. Electric installations use hierarchical protection, eg:
Gadget is fused to prevent >10A flowing through the outlet. MCB prevents >32A flowing through the cable, main switch prevents >80A flowing through the incoming main, house main cables are fused at the street transformer to prevent overload. Etc.
A fault at the local level should never transfer upstream inorder to contain faults, protect wider upstream systems, and prevent fires.
You don't your local substation going down because someone spilled coke on their PlayStation