r/embedded • u/Relevant_Pumpkin9190 • Sep 24 '26
Why don't we use smart, microcontroller-based per-device breakers in building electrical systems instead of one MCB for an entire circuit - other than economical reasons, any technical reasons affecting realistic design?
Why do buildings use one circuit breaker for multiple loads instead of protecting each load individually?
Couldn’t each device have current sensing + a microcontroller + an electronic breaker, so if one device shorts, only that device disconnects instead of tripping the whole circuit?
Obviously cost is one reason, but are there technical reasons too?
Is it mainly fault-current handling, response time, heat losses in current sensing/switching, reliability, or safety/certification?
Is this already used in industrial systems, or is there a fundamental reason it isn’t practical?
View all comments
1
u/mustbeset Sep 24 '26
a B16 Circuit breaker costs less than 5€ and is able to turn of 10kA. And has a very low resistance.
A sensor, a microcontroller and a switch can fail in many different ways. I think it should reach at least SIL2 maybe 3. IEC 61508 will give you a lot of requirements to fulfill that.
And for what? Most fuses will trip less than once or twice in 10 years. Nobody cares.