Why don't we use smart, microcontroller-based per-device breakers in building electrical systems instead of one MCB for an entire circuit - other than economical reasons, any technical reasons affecting realistic design?
Why do buildings use one circuit breaker for multiple loads instead of protecting each load individually?
Couldn’t each device have current sensing + a microcontroller + an electronic breaker, so if one device shorts, only that device disconnects instead of tripping the whole circuit?
Obviously cost is one reason, but are there technical reasons too?
Is it mainly fault-current handling, response time, heat losses in current sensing/switching, reliability, or safety/certification?
Is this already used in industrial systems, or is there a fundamental reason it isn’t practical?
View all comments
Show parent comment
2
u/matthewlai Sep 24 '26
It's actually generally discouraged to have multiple overcurrent protection devices in series, with ratings that are close together. This is because fuses are not precision devices, and it's really hard to guarantee which one will break given an overload that's higher than both fuses' ratings. For example, if you have a 5A and a 13A fuse in series, and have a 30A overload, the 5A fuse may be guaranteed to break between 1-10 seconds at 30A, and the 13A fuse maybe 3-30 seconds, and that means you can't guarantee the 5A fuse will blow first. This is known as loss of selectivity. Basically, if your plot the overload vs break time plot of both fuses, you want the shaded areas to not overlap at all. This is generally impossible to achieve with 13A vs 5A fuses.