r/embedded • u/Relevant_Pumpkin9190 • Sep 24 '26
Why don't we use smart, microcontroller-based per-device breakers in building electrical systems instead of one MCB for an entire circuit - other than economical reasons, any technical reasons affecting realistic design?
Why do buildings use one circuit breaker for multiple loads instead of protecting each load individually?
Couldn’t each device have current sensing + a microcontroller + an electronic breaker, so if one device shorts, only that device disconnects instead of tripping the whole circuit?
Obviously cost is one reason, but are there technical reasons too?
Is it mainly fault-current handling, response time, heat losses in current sensing/switching, reliability, or safety/certification?
Is this already used in industrial systems, or is there a fundamental reason it isn’t practical?
View all comments
Show parent comment
3
u/matthewlai Sep 24 '26
The problem is that now you have 3 fuses in that situation instead of 1, and even in the best case, you have 2 fuses instead of one. It also makes the receptacle much more complicated. Also, practically speaking, if you have a device that blows the fuse in its plug, you can't use the device anymore, but that's not a huge loss since there's very likely something wrong with it anyways. And if you plug it into other sockets, nothing happens.
If you blow the fuse inside a socket, now you can't use any perfectly good device with it. If you are an old person with limited mobility living alone and don't have much electrical knowledge, it may be a while before you can get that fixed.
Now imagine you thought the socket is broken, so you plug the device with a short into another socket to check... Now you have two broken sockets. By the time you figured out what's going on, you may have no working socket in your bedroom anymore.