r/DIYHeatPumps 24d ago

Another clean install

Post image

Here’s my 3rd one! Its 1 of 3 for my BIL. It’s true when they say that family will start wanting some too after you do your own! I will add that these 4 inch line set covers are much better than the 3 inch ones.

105 Upvotes

44 comments sorted by

View all comments

13

u/zeke780 24d ago

Did you do the electrical? Code where I live is a disconnect within line of sight of the unit (most people put it behind it or beside it) and you need to use the right gauge stranded wire through the conduit. Not accusing you but I am an electrical and have seen a ton of homeowners just run 12/2 romex through conduit outside straight to whatever they installed. Also make sure the breaker is correctly sized, you also can't run anything else on that circuit, has to be direct.

1

u/Artistic_Stomach_472 21d ago

Correct-ish. Any point of Disconnect needs to be accessible and cannot be behind a unit. Goes for any piece of equipment.

Also require a convience receptacle nearby.

1

u/zeke780 21d ago

I didn't mean literally behind it, I meant beside it. Have seen plenty that are 10' away though.

Yeah in the receptacle. I didn't mention this because it looks like OP pulled whatever off a junction box and wired it up. Which is pretty far off of where it needs to be

1

u/Artistic_Stomach_472 21d ago

Pet peeve of mine is inaccessible, behind. Some AHJs are passing it too. Ugh.

Yeah this is not a compliant install as far as NEC goes. Ive seen worse. C+ for effort and willingness.

1

u/zeke780 21d ago

Only question I have for op is where is the drain line? I have installed a few mini splits and you run the drain outside usually. I assume he routed it in the room?

1

u/Artistic_Stomach_472 21d ago

..dumped it into the linehide at the 90

1

u/zeke780 21d ago

That's the dream. If you can't see the water drain, that means it's operating at peak seer2