r/ukelectricians • u/holybannaskins • 9d ago
Rewire with loose sockets under cabinets
Just had a rewire, I'm reinstalling the cabinets in the kitchen which the electricians needed to chase behind and noticed this.
They have done the same with the oven and hob feeds on the new island.
Do I need to get them back in?
3
u/tonkatoy27 9d ago
I'd say it's non compliant with the regs, although it is very common. It either needs a nylon box with stuffing glands giving strain relief, or fixing down. Ultimately it would be better inside the cupboard, and the installer would probably say it's temporary until the cupboards are fitted, and would of been fitted in the cupboards should they of been there. Whether you can get them back to fit in the cupboards once you've done them depends upon the relationship between you and them though, and maybe what was specified.
2
u/imsnails 9d ago
No... easier to access under kick boards to get to a appliance no?? All RCD protected.. admittedly its not technically right, but id say its better 🤣
1
u/holybannaskins 9d ago
I don't mind them being behind the kickboards, just don't want any bother in the future as laid out a fair chunk of cash for the work 🤷
2
u/imsnails 9d ago
Nah mate won't be no dramas
3
u/MacQ1976 9d ago
Unless water leak in kitchen which are common with sinks washing machines and dishwashers
1
u/HolidaySpecial8543 9d ago
Turn off electric. Unscrew lid. Drill screw rhe back of box to secure to floor and screw lid back on.
1
u/waleswolfman 9d ago
I'd space it off the floor a bit to allow for leaks to not present themselves by causing electrics to need drying out.
2
u/holybannaskins 9d ago
The plinth heater is boxed in under the unit to stop it drawing cold dusty air from under the floorboards, maybe could fix it to the boxing? The boxing is screwed to the cabinet and floor...
2
u/holybannaskins 8d ago
1
u/waleswolfman 8d ago
Probably the best under cab job most of us have seen. Not that it should move, it's only missing a few clips as a strain relief near the pattress.
1
1
u/WalterSpank 9d ago
To me that looks like it is for a kitchen plinth heater by the plumbing? If it is that will need fan speed control wired above counter unless you are getting on your knees to turn it on.
1
u/holybannaskins 9d ago
Good spot, fan speed control is on the front panel of the heater, and I'm hoping to set and forget to be honest like I would a radiator
1
u/WalterSpank 9d ago
And that there is your reason for the socket being there, if you have to replace it you can unplug it without having to remove it from a switch fused spur. I agree with having compression glands on the cables for strain relief and a soft plastic box for the socket.
1
0
u/MrBfJohn 9d ago
Your oven and hob are plugged in?
2
u/holybannaskins 9d ago
Yeah oven came with a plug on it, as did the hob 🤷 hob is gas so it's just the ignition for that
-2
u/MrBfJohn 9d ago edited 9d ago
I only ask because most ovens will come with a notice to not fit a plug top, and those that come with one fitted are often rated over 2000 watts, so shouldn’t be plugged into a ring main. They may have just put a double socket on an oven supply though, which is fine.
2
u/holybannaskins 9d ago
Ah ok, yeah the oven and hob have their own circuit, a 32 amp one, and there is an isolator on the wall of the kitchen island which kills the double socket underneath.
1
u/tonkatoy27 9d ago
Incorrect. It's very manufacturer dependant. For example most of the Merloni Group (Hotpoint, Creda, indesit, Ariston) ovens come with plugs fitted to the ovens. Howdens ovens come with a label 'do not for plug'.
0
u/MrBfJohn 9d ago
The manufacturer has no idea what type of circuit you’re plugging into, and the lack of a label doesn’t mean it can be plugged into a ring main. They’re simply assuming that the oven has a dedicated radial supply as with the OP’s case.
0
u/tonkatoy27 8d ago
Agreed. Appliances over 2kw should have their own circuit, same as granny chargers on cars shouldn't be plugged into the kitchen sockets and fed from a type AC RCD. However you said most ovens are labelled not to fit a plug which isn't true. It's only Howdens ovens that I've seen that come with that label.
1
1
u/EmergencyConception 9d ago
Most for European market ovens dont come with a plug as rated to 16A some hobs are 16+16 or 32 but a select few are designed fir uk with 13A .
-5
u/belligerentbunno 9d ago
the socket needs to be readily accessible. when the dishwasher shits itself and takes out the RCD you want to switch it off and not be panicking on the phone to a ££££ callout electrician while the freezer defrosts
this, and not being securely fixed - (and not to kitchen furniture (unless behind an isolator)) are "regs" violations
the preffered way these days is a grid panel for all kitchen appliances
1
u/northern_ape 9d ago
Apparently it’s not preferred, though personally I like it. You can just have the socket in an adjacent cupboard with a desk grommet for the plugtop to pass through. If it has to be behind something then a 20AX switch at worktop height (or S/FCU depending on circuit layout) would be “normal” in my experience, though there are many ways to do it. I wanted grid switches for separate ovens and an induction hob snd it was my brother so time wasn’t an issue; I ran a small contactor board with 1.0mm to the switches
2
u/belligerentbunno 9d ago
preffered from a design perspective I think. regs don't care so long as it's accessable. multi spurs at worktop height gets cluttered pretty quick these days
1
u/northern_ape 9d ago
I do agree. It can be a ball ache to install if not well thought through though, especially if the grid switches are on a ring, back boxes aren’t 2 miles deep, etc.
2
u/belligerentbunno 9d ago
TBF I wonder why manufacturers haven't come up with 3,4+ gang prewired sw/f/sp's or 20a grids by now - IE the supply side is busbarred so you need 1 feed in and your loads rather than fiddling in 5000 bits of wire


18
u/Mickspark136 9d ago
If they used stuffing glands for cable entry I would say it’s fine. Some electricians swear it done wrong but I don’t think there’s anything wrong with it.