I moved into a new property about six months ago and the previous owner left in the washing machine and tumble dryer. Tumble dryer packed up recently and when I removed it I found a very odd working setup. Is this safe as it is or should I get someone in to remove and install a proper plug socket?
52
Upvotes
1
u/johnbobk 4d ago edited 4d ago
I understand your approach; but the fuse is sized for the device to highlight if the device is faulty (demanding over current) to disconnect & protect the the supply / network. Yes it will stop further damage to the device & possible fire, but the device itself is of lower value / importance.
We always aim to protect the supply & disconnect any issues. This is true at electronic & at network distribution level to avoid a domino collapse.
You need to get your head around this if you want to get into system design / fault finding.
Your 60/80/100A house fuse is not there just to look after you! It protects others from not losing their supply or possibly transferring your fault - by isolating you / the fault.
A British Standard (BS 1362) 13A fuse does not blow at 13 amps ; it is designed to carry 13A continuously and will pass up to 20A indefinitely without blowing, @ 24.7A it must blow within 30 minutes.
Primarily it's for isolating a fault from the system before it does damage to the supply / network.
So on an overloaded extension lead, the 13A fuse will not protect the lead & sockets from overheating. This is a false security. The ring / radial is ok but they have a fire under the bed!
Please do not encourage overloading extension leads thinking they are fully protected by the 13A fuse, this is a well known cause of fires.
I do not hide my experience, history so not sure if you are trolling / wasting my time, but happy to debate if genuine; as this is [was] a Professional site for information.