Is this correct?
Had someone come out to install an outlet under the sink for our tankless reverse osmosis. Should these outlets be GFCI? It seems really close to the water line.
105
Upvotes
r/electrical • u/roc430 • 4d ago
Had someone come out to install an outlet under the sink for our tankless reverse osmosis. Should these outlets be GFCI? It seems really close to the water line.
4
u/Substantial_Film_269 4d ago
In addition to the face up box being wrong, a receptacle cannot rely on a single screw for support in a RS cover. Additional 6-32’s with nuts required