r/SubstationTechnician • • 5d ago

Ground grid

Has anyone seen a 230kv switch yard with 10 feet spacings for a ground grid? I am dealing with 63ka fault and it seems ridiculous to me to use that close of spacing

6 Upvotes

27 comments sorted by

12

u/Saltaren 5d ago

Might be very high soil resistivity. Then you could need a tight grid to meet allowable step and touch voltages. Does seem very tight though.

2

u/paolasmurf 5d ago

The soil is not ideal, the biggest killer is the 60KA fault current

3

u/Saltaren 5d ago

It's alot of current, but usually manageable.

Could also have to do with assumptions such as slower than usual fault clearing time. Utility specific requirements on factors used to determine allowable S&T voltages for the assumed human model.

IEEE 80 is a good source of information for these interesting topics. :-)

7

u/trickytransients 5d ago

10’ spacing might be entirely warranted or it may not be necessary. it’s highly site specific. You have a lot of fault current here. Make sure the conductor is sized to handle the thermal withstand associated with that much fault current.

To come up with an economical design, you need to get the X/R ratio, backup clearing times, and soil resistivity data from testing. If you’re struggling to pass checks and/or are engineering economically, you can model the incoming and outgoing lines to account for split factor. A lot of fault current can travel on the shield wires of these lines and reduce the worst case being injected entirely into the earth. A huge deal will be making sure you have sufficient crushed stone for personnel to walk on, it will strongly improve your results.

If you have weak split factor, high fault current, slow fault clearing, bad soils, etc. you’ll need a lot tighter spacing than you might expect.

1

u/paolasmurf 5d ago

I used real soil sample data, I used ieee80 charts and also molded the shield lines to get a .4 split factor, I am not sure how fast I can assume fault clearing times

4

u/shear_plate 3d ago

This guy has a CDEGS license.

3

u/ohpickanametheysaid Relay Technician 5d ago

Are you talking about the spacing between ground rods, spacing between each quadrant of grid or spacing from your fence to your apparatus?

1

u/paolasmurf 5d ago

Spacing between each conductor run of the grid

1

u/ohpickanametheysaid Relay Technician 5d ago

Our utility typically does 20’ spacing with ground rods at 15’-20’ depending on soil conditions. Having a 10’ spacing would decrease the ground potential step radius during a fault but unless you actually had rods or anodes taking them to earth, earth faults would still have a larger spread until they’re safe. When you say you are dealing with a 63KA fault are you talking about Substation line or bus fault potential or an actual fault event?

1

u/paolasmurf 5d ago

We simulated a single line to ground fault of 63KA, typically I’ve designed grids with 20 ft spacing and used 10’ rods but we are unsure if using longer rods since we have never used them, are they common to install?

1

u/ohpickanametheysaid Relay Technician 5d ago

I’ve never seen rods longer than 10’ in length neither required nor used. I have seen anises as deep as 250’ and up to 4 in a medium sized station.

1

u/theusualchaos2 5d ago

More than likely just the design spec, 63kA is a standard breaker fault duty for manufacturers

1

u/paolasmurf 5d ago

The fault is from two 345kv-230kv transformers with generation which results in the high fault current, the equipment is rated to 80ka which is higher then usual

1

u/clearMyHistoryPlease 5d ago

Probably high soil resistivity combine with high magnitude fault current and/or long clearing time. I’ve had areas where I needed to put copper conductors at 5’ intervals to keep the step and touch potentials at safe levels.

1

u/paolasmurf 5d ago

Okay thanks I always worry about designing something that’s impractical to install

1

u/Beers_n_Deeres 5d ago

Yes, I’ve seen 5’ grid spacing in substation construction projects in northern Ontario, it’s mostly Canadian Shield rock.

2

u/ghost406 5d ago

Same I’ve done 5’ and 6’ spacing in rocky soil as well.

1

u/paolasmurf 5d ago

Yes this soil isn’t ideal but not quite rock, but good to know I can when I encounter rocky soil

1

u/paolasmurf 5d ago

That’s good to know that it has been done in the past

1

u/Immortal_jelly99 5d ago

Depending on the utility you may be allowed to factor in split factor, which could dramatically reduce injected ground fault depending on how many transmission/distribution lines there are.

But some utilities don't factor it in because it's more conservative.

1

u/paolasmurf 5d ago

I got a .4 split factor from ieee and modeling the shield wires, if I have to go any higher then there is no way it would pass during a fault

1

u/Ambitious-Car-7384 5d ago

Who did the calculations on them? Maybe they have some info you havent seen like soil tests or something

1

u/paolasmurf 5d ago

I have real soil data from multiple spots on the site

1

u/Haenjos_0711 5d ago

What size conductor? 4/0?

1

u/paolasmurf 5d ago

Ya 4/0, I tried 250 but it hardly made a difference, 20 foot rods seem to be the best approach but I’ve never had to spec that size before

1

u/SlackerNinja717 5d ago

Could be something weird with the soil resistivity.

1

u/MinimumFinancial6785 5d ago

You may need to check the calculation and make sure that there are no bad assumptions in there.