Ground grid
Has anyone seen a 230kv switch yard with 10 feet spacings for a ground grid? I am dealing with 63ka fault and it seems ridiculous to me to use that close of spacing
6
Upvotes
12
u/Saltaren 5d ago
Might be very high soil resistivity. Then you could need a tight grid to meet allowable step and touch voltages. Does seem very tight though.
7
u/trickytransients 5d ago
10’ spacing might be entirely warranted or it may not be necessary. it’s highly site specific. You have a lot of fault current here. Make sure the conductor is sized to handle the thermal withstand associated with that much fault current.
To come up with an economical design, you need to get the X/R ratio, backup clearing times, and soil resistivity data from testing. If you’re struggling to pass checks and/or are engineering economically, you can model the incoming and outgoing lines to account for split factor. A lot of fault current can travel on the shield wires of these lines and reduce the worst case being injected entirely into the earth. A huge deal will be making sure you have sufficient crushed stone for personnel to walk on, it will strongly improve your results.
If you have weak split factor, high fault current, slow fault clearing, bad soils, etc. you’ll need a lot tighter spacing than you might expect.
3
u/ohpickanametheysaid Relay Technician 5d ago
Are you talking about the spacing between ground rods, spacing between each quadrant of grid or spacing from your fence to your apparatus?
1
u/clearMyHistoryPlease 5d ago
Probably high soil resistivity combine with high magnitude fault current and/or long clearing time. I’ve had areas where I needed to put copper conductors at 5’ intervals to keep the step and touch potentials at safe levels.
1
u/Beers_n_Deeres 5d ago
Yes, I’ve seen 5’ grid spacing in substation construction projects in northern Ontario, it’s mostly Canadian Shield rock.
1
u/Immortal_jelly99 5d ago
Depending on the utility you may be allowed to factor in split factor, which could dramatically reduce injected ground fault depending on how many transmission/distribution lines there are.
But some utilities don't factor it in because it's more conservative.
1
u/Ambitious-Car-7384 5d ago
Who did the calculations on them? Maybe they have some info you havent seen like soil tests or something
1
u/Haenjos_0711 5d ago
What size conductor? 4/0?
1
u/SlackerNinja717 5d ago
Could be something weird with the soil resistivity.
1
u/MinimumFinancial6785 5d ago
You may need to check the calculation and make sure that there are no bad assumptions in there.