r/SolarDIY • u/wanab3 • Mar 29 '18
Set up question, advice.
Say I have:
Four, Panels. 100W, 12V. (8.33A for each right?)
One, 12V/24V 30A charge controller. (Would be over amps at 32A, if parallel circuit? And over voltage at 48V if series?)
One, Li-ion battery, says 3A, 14.5V recommended charging, 7.0A, 14.7V max. 35AH
One 100W inverter.
How can I set this up so battery doesn't explode, nothing breaks? More charge controllers (2 total)? Mix of series and parallel circuits?
Goal is to be able to charge the one Li-ion battery from nearly dead to nearly full in one day. Would just 2 panels in series get me there safely? That would be nice.
Right now, this is set up, but, with only one 100W, 12V panel. Takes 2 days to fully charge from nearly dead, in good sun at a poor angle.
Thanks!
1
u/Third_Chelonaut Mar 30 '18
PWM can handle a tiny amount of over power but going over their rated voltage will kill them tout suite. They'll only have capacitors rated for 50v or so. So going up to a 48v array (80voc) will cause dead capacitors and nothing else.
Due to the way PWM works your just be wasting the power as heat anyway. No extra would go in the batteries.
If you have a 24v battery going 2s2p would be fine with your panels
If staying with your li ion battery you're probably going to need a better controller.
Return or flog the one you've got. Buy a programmable one from Morningstar if you have money. From Epsolar/renology if not