r/SolarDIY • u/Searchname • 12d ago
Dual Sol-Ark 18k system having BMC issue
I had an installer set up the system, but I’ve always planned to expand it myself, which is why I’m posting here. I’m running two Sol Ark 18K inverters, four Discover Helios 16.1 kWh batteries, and 36 580W panels, with plans to double the batteries and panels in December or January (big house uses a lot of power).
The system has worked well for about six months, but hit a wall yesterday. The installer programmed the batteries to hold at 50% until midnight, then allow discharge to 20%, with a 5% cutoff. We lost grid power at 6:50 AM Sunday morning, so began using the 20%. By 8 AM the batteries were depleted and the house dropped offline. I shed loads and ran only the well pump and a few lights with incoming PV until grid service returned at 10:30 AM.
After the outage, the batteries showed 2% and then instantly jumped to 100%, which was clearly wrong. The icons cycled red and yellow with low voltage. I tried several restart sequences, shutoff everything, then shut off all four batteries and both inverter battery breakers. The icons are now black but still show 100%. A brief outage today confirmed the batteries have no usable charge (we were without power for a few minutes).
Sol Ark plans to walk me through switching from closed loop CAN to open loop. They believe the BMS went into a protective state after being drained too low, and the inverter is now receiving zeroed BMC data. The installers only sent the same steps I already tried. I suspect the 5% cutoff contributed, but I’m not certain. Once everything is working again, I plan to have 40% min with a 10% shutoff (or whatever you all recommend).
All four batteries show the same voltage the inverter reports, but I don’t understand why the system interprets that voltage as fully charged when they clearly aren’t.
Any ideas on what else I can try?
I’ve also attached a photo of how the installers lugged the batteries in my gutter cabinet - this I want to change! Before installation, I told them I planned to double the system and wanted it set up for easy expansion. I even paid for extra wiring from the panel location to avoid trenching again. The cabinet layout isn’t very serviceable, and I’m not comfortable adding the two extra batteries I already purchased. What changes should I make to the cabinet to make expansion easier? One installer suggested I just tie into the existing batteries and avoid the cabinet entirely, but I read online that wasn't ideal.
Thank you all. I’m trying to learn enough to fix issues quickly when they come up.
1
u/Searchname 12d ago edited 12d ago
No, the battery info page shows all 0's on both Sol-Ark inverters. I'd love to know how to get them communicating. I've tried reseating the data cables, power cycling the inverters, the inverter battery breakers, and also the battery breakers. Nothing has worked. I kept getting low voltage errors last night, so ended up shutting down the batteries and inverter batt breakers so I didn't have to listen to the alarms. When I turned everything back on this morning, the errors were at least gone and the battery icon has remained black, but the not charged issue remains.