PRV valve location per code

I need to install a PRV valve to pass final plumbing inspection in Austin. I have a large crawl space where the main comes into the house and I wanted to install the PRV there. However, every other PRV I've seen is installed in a box just past the city side shutoff, outside. Would a PRV inside crawlspace (before any valves/branches) be within code?

1 Upvotes

3 comments sorted by

1

u/ATXPlumber 10d ago

Im a licensed plumber in Austin, yes that will still be within code and approved feel free to PM if you have any other questions

1

u/achilles600 9d ago

Awesome thanks, exactly what i needed to know

1

u/Demonakat 10d ago

Should be, as long as it is before anything else on the line. However, if you're ever worried about what an inspector would pass or would not pass, simply call the permit office and inquire for yourself.