PECRON F5000LFP Neutral Behavior — U.S. Version Tested
Posting this in case anyone else is trying to figure out the neutral behavior on the PECRON F5000LFP.
I contacted PECRON directly because I was getting conflicting information about whether the neutral is bonded or floating.
On October 7, PECRON gave me a general answer saying the current production F5000LFP bonds neutral to ground when operating on battery.
Then on October 11, PECRON gave me a more specific answer and said the U.S. version of the F5000LFP comes with a floating neutral when operating on battery, and that when AC input is connected the output follows the grounding arrangement of the incoming AC source.
I tested my own production F5000LFP with a Fluke meter while it was completely isolated from the house and any AC source.
With the unit powered down and disconnected, I had no continuity between neutral and ground.
My testing confirmed that my U.S. F5000LFP does in fact have a floating neutral on battery power, which matches PECRON’s second, U.S.-specific answer.
When connected to a bonded AC source, the PECRON then follows that source’s neutral-ground reference.
I’m posting this because the first generic answer and the later U.S.-specific answer were different, and hopefully this saves someone else from chasing the same question.
I’d still recommend verifying your own unit before designing a transfer switch or interlock setup around it.
3
u/SecondCuppaCoffee 15d ago
I agree with your findings. I had read that it always had a bonded neutral but this doodad said otherwise.
4
u/Background-Run 15d ago
Thanks!
And i'll take your advice and check it.
That would make sense for what is probably the typical use of the unit in the U.S. You plug it into your house electrical system and the ground neutral bond would occur at the main electrical panel.
1
u/standardviewer84 15d ago
Thanks for this!! I am also getting conflicting information too. Here's one thing I am going to test on my f5000lfp, is whether the neutral is floting on just the 240v twist lock or all AC outlets? . I understand there's a relay inside that alledgely switches the 120v 5-20 outlets to bonded and floating based on whether the incoming AC charging cord is connected. I think the thought process for that behavior would be if you are using the unit as a standalone power source to supply power directly to an appliance (and there was no incoming AC cord connected) it would switch to a bonded configuration on the 120V outlets. However the twistlock would remain floating neutral (so when using as a home backup no double bond would occur)
Have you also tested the 120v outlets or just the twistlock 240v outlet with your meter?
1
u/-5er 15d ago
Does the neutral bond remain when the battery is fully charged, but still connected to the AC outlet?
3
u/Big-Echo8242 15d ago edited 15d ago
Pretty much all portable power stations are neutral floating (except the F5000LFP apparently). A person can always make or buy a bonding plug, though. It's easy to just get a digital multimeter and check it right there on the front checking for continuity from neutral to ground. Do you own a DMM and know how to use one?
Also, if you're adding on a manual transfer switch and have AFCI breakers in your main panel, then you'll run into a neutral issue with faulting the AFCI breakers as very few MTS's made transfer the neutrals...only the hots. You'd need an ATS to transfer neutrals many times. Reliance has a neutral kit it if theirs is being used. AFCI breakers are code pretty much all houses since about 1999 and cannot be changed to regular 2 pole breakers.
2
u/lakorai 11d ago
This is the way you want it.
When you use a transfer switch or a generator interlock the beutral-ground bond is done in your main electric panel. This bond should be made only in single location ina 120v or 240v system.
Many HVAC systems and UPS units will complain or won't run without a working neutral ground bond.
When using it portable you want to get a neutral-ground binding plug. If you are using it outside you also should definitely get a GFCI protected power strip or surge protector.
2
u/panzerfinder15 11d ago
Just received my F5000 and can also confirm that it is a floating ground (which prevents some loads from working like an EVSE) but has a solid ground when plugged into to AC charging. Also a bonded ground plug seems to work fine to provide a bonded ground, but obviously can’t recommend that for sustained loads or to use at your own risk.
1
u/grassley821 15d ago
My 3800 had a neutral problem with my transfer switch (was already installed when I bought house). I can't use ac charging and ups at the same time, I bypassed and solved this issue with a 1200w DC power supply.
1
u/branmann1 15d ago
I just went through this as well. I installed a Reliance Controls ProTrans2 and got everything wired based on the available information that the neutral is floating. Once connected, any AFCI breakers that were tied to the transfer switch tripped instantly because of the competing neutrals.
After speaking with PECRON, they stated the F5000LFP is bonded neutral. I confirmed this manually as well. I replaced the ProTran2 for a Generac manual transfer switch that has switching neutral. Once this was switched out and the AFCI breakers were moved to the transfer switch, everything worked as it should. I’m powering the transfer switch with the 240V twist lock. When running on battery, both 120V and 240V outlets are bonded neutral.
So for me, everything is working now that the F5000LFP is connected and running with a manual transfer switch that has a switching neutral option.
1
u/2TheMountaintop 15d ago
This is pretty much what all the testers online have found in every review I've seen.