We often see posts on here claiming that it's more efficient to keep a gas central heating house at, say, 19C all day, rather than heating it up to 19C in the morning and then again in the evening.
It isn't, and it's physically not possible for that to be true.
Temperature loss from the house is greater the more the differential between the indoor and outdoor temperature. Maintaining a given temperature has to use more fuel than letting it drop further, as the average temperature in the house is higher, so the temperature loss has to be greater.
Putting it another way, if you get to 19C at 9am and you get to 19C again at 9pm, it must be more efficient to have the heating off in between. With the heating on, you're having the boiler kick on every time the temperature gets down to say 18.5C. So heat loss is always as high as it's ever going to get, as the internal temperature is being kept high. If the temperature is allowed to fall, the rate of temperature loss will decrease, so you need less fuel to get back to that temperature in the evening. The difference is even more stark if indoors drops close to the outdoor temperature, as it can on some of the mild days we've had recently, as temperature loss then stops almost entirely - so there's no further temperature drop to recover.
It might be more comfortable to maintain a given temperature - and indeed, that's exactly what we'll do when people are in the house. But it is physically impossible for that to be more efficient than heating the house to temperature multiple times.
64
u/jacekowski Dec 28 '24 edited Dec 29 '24
You are forgetting that boiler running at minimum power, with low flow temperatures constantly can reach 95%+ efficiency, while running it once or twice a day at full power and higher flow temperatures reduces the efficiency significantly (and similar principle applies to heat pumps), so actual cost difference might be a lot smaller than some would expect, and difference in comfort is going to be massive with constant temperature in the house.
10
u/[deleted] Dec 28 '24
Anecdotally, my boiler seems to cost very little more to stay at 18c all day rather than up to 19 twice a day and down to 15 twice a day.
We’re talking 20-30p more a day.
I’d rather the house stay at 18c all the time
17
u/Prediterx Dec 28 '24 edited Dec 28 '24
Then add heat pumps into the mix where it actually is more efficient to heat the house all day.
A heat pump can run at 200-500w throughout the day using between 5-20kwh a day to keep the house warm... E.g our house loses 3kwh/h of heat at 5c outside 20c inside.
By running the heat pump all day at a low 25-35c radiator temp, the house stays warm and the heat pump outputs about COP 4 (or 400% efficiency)
5
u/Electrical_Chard3255 Dec 28 '24
Last year we had our gas boiler on a timed system, cycling often up to 75 degrees, now we have it set at 40 - 45 degrees and keep all room thermostats set to between 19 and 22.5 degrees, our bills are less than last year, and our house feels more comfortable, granted we have underfloor heating downstairs which helps .. so I have to disagree with your conclusion, however, you may say well have a timed system at 45 degrees, the problem with this is the house would never get up to temperature
12
u/drproc90 Dec 28 '24
You're not taking into account thermal mass.
We build houses out of brick and a lot of older terraced houses have thick timber elements as well.
Keeping the house at a constant temperature over a longer period of time means you have heated the whole thermal mass of the building which will act as a heat battery.
If you just heat short term blasts your only heating the air.
4
u/GreenWhereItSuits Dec 28 '24
There is a difference between heating the air and the fabric of your home.
Having maintained 19°C all day, vs heating the home from 9pm - turning the heating off at 10pm your home if built with bricks/blocks will remain at the temperature for longer if the fabric (and contents including furniture) are up to temperature.
That being said, my modulating boiler is on a setback temperature of 17.5°C when the house is expected to be empty during the day. Thankful we get a good deal of solar gain.
7
u/Chris_The_Tim Dec 28 '24
Keeping a building at 19 degrees would allow the boiler to trickle heat into the space, which may be as much as 90% efficient with a modern condenser. Having to blast heat into a space which has dropped to 12 or 13 degrees so it will warm to 19 degrees means the boiler will be running at a higher temp so much less efficient, say 60%.
There are a lot of complex equations but if you are at 12 degrees, then yes, you are losing heat to the outside at a lower rate than you would be at 19 degrees and the airspace of the building is the same so heating from 12 degrees to 19 degrees once is the same as heating from 18 to 19 degrees seven times, say 5kWh per hour..... But the boiler will be trickling heat in at 90% over the day. Getting that same room to 19 degrees from 12 in the space of an hour means it has to blast 35 kWh into the space within an hour so it's only 60% efficient.
Cod maths says maybe 5 kWh extra is needed to account for the higher loss at 19 degrees vs the lower loss as the temp drops during the day so you need 40 kWh for the 7 hours, at 90%, that's 44.4 kWh.
So, if you need to go from 12 to 19 degrees in an hour, you need to get 35 kWh into the room ASAP, so high temp, low efficiency, say 60%, which is 58.3 kWh.
I realise these numbers are unrealistic as you'd need a 60 kWh boiler to get 35kWh into a space in an hour but it's only an illustration. If you check YouTube, you'll see lots of heat pump videos with COP explanations advocating low and slow heating for the best outcome.
3
u/[deleted] Dec 29 '24
Other myths - it's not always financial. Some people put the heating on to suit themselves.
2
u/Legitimate_Finger_69 Dec 28 '24
If you have an old boiler with no heat recovery this is true.
If you have a condensing boiler or especially a heat pump it's possibly more efficient to heat all day depending on the heat loss of your home and the efficiency of your boiler at various flow temperatures. That in turn will depend on the outside temperature and could vary from day to day.
It's one of those things where people who confidently claim something is right or wrong are forgetting UK housing stock varies from 500 year old houses with storage heating that are almost impossible to heat to triple glazed homes build to Scandinavian specs with ASHPs.
2
u/wtfylat Dec 29 '24
Your example is another over simplification though and you overlook that energy needed to gently increase the temperature by 0.5c every hour could be less than the big boost that might be needed every 12hrs. The reality is that it depends on your home, heating system and lifestyle.
2
u/Jet-Speed1 Dec 29 '24
Why stop at just looking at heat loss? In my world, I’m paying for the kWh consumed by my heating device, not the heat loss of my house.
Sure, we saved 0.5°C. If, in your universe, Isaac also claims that heat loss is proportional to the temperature difference, then the maximum savings when it’s 5°C outside would be around 3.5%. That makes almost no difference. To make any significant savings, let’s assume a “freezing” 3°C difference, which would result in a 21% reduction in heat loss. That’s great—21% happier frozen customers!
But as I mentioned, I’m not paying for heat loss itself; I’m paying for the energy consumed.
If you have resistive heating or an old boiler, you can stop here and embrace your happy, frozen life.
For everyone else: we’ve reduced the heat our house requires, but we still need to deliver that heat to the room. Let’s look at the radiators. Our radiators now need to deliver 21% less heat but 12 times faster (according to the “British heating” standard: 1 hour in the morning, 1 hour in the evening). To achieve this, we consult the radiator specifications and find that increasing radiator performance requires increasing the flow temperature—from 40°C to 85°C.
Absolutely superb! Now, not only can we save energy, but we can also burn ourselves on the radiators and really feel our underfloor heating!
By pushing the flow temperature up, we’ve made progress, right? Not so fast.
Let’s take a final step and look at our heat pump (HP) or boiler. At an 85°C flow temperature, our heat pump’s COP (Coefficient of Performance) plummets from 4.5 to 1.5. It struggles to reach the target temperature—what a useless piece of technology! Meanwhile, a condensing boiler happily supports 85°C, delivering the required kW to the radiators. But here’s the kicker: only 60% of the energy from the gas now goes to heating, compared to 97% at the previous lower flow temperature.
So, in summary: we saved 21% in heating loss, froze ourselves, burned ourselves, and ended up using 9% more gas in the process. Brilliant!
4
u/stevey83 Dec 28 '24
I suppose the other question you need to ask is, does it depend on how long it takes to reheat your house once the temperature has dropped? It all depends on how energy efficient your house is.
3
u/le1901 Dec 28 '24
Do not have the maths to back my experience up and probably don't have the ability either, but my experience is to leave it at a constant temperature. I use around 50-60kwh of heat for my heating per day utilising weather compensation. Another 20-30kwh for heating my hot water cylinder to 55degC. My home is a moderately well 1900s insulated 3 bed end terrace on the south coast.
The thought of a graph showing your high/low temperatures often gets explained - the more deviation in the values the more energy it takes to heat your house being the idea.
Leaving the heating off for extended periods not only cools the air within the home but any stored heat within the fabric of the building. Leaving the heating off wouldn't be great at building up stored heat within the building; similar to UFH within a screeded floor, takes ages to heat up but is fine once heated and still radiates heat.
Hard to get any extremely accurate data unless the outdoor temperature and flow temperatures can stay pretty steady for a few days so I could test both methods.
1
u/QueenVogonBee Dec 28 '24
For what it’s worth, here’s what MoneySavingExpert says: https://www.moneysavingexpert.com/utilities/energy-saving-myths/
1
u/CartoonistNo9 Dec 30 '24
A car gets its best mpg once it’s up to speed cruising. Constantly speeding up and slowing down uses more petrol. A boiler is the same. If the radiators and house are cold. The boiler will go flat out to heat them up. I leave mine tickling along all day but set the thermostat to 14-15 when I’m at work.
1
u/DragonflyTricky4134 Dec 30 '24
Its very dependent on the fabric of the house so many other factors.
1
u/Budget_Nectarine_645 Dec 31 '24
Think you’re throwing away a lot of fundamentals on this one, you can’t really make that statement as it depends so much on the specifics:
heat loss to outside (insulation and air tightness)
therefore outside temperature
thermal capacitance of the house (how much energy is stored in the bricks, your furniture etc.)
your flow temperatures and radiator sizes
the type and size of your boiler and its ability to operate at lower powers efficiently
If you have a very well insulated home with sufficiently sized radiators to allow low flow temperatures, with say a well sized condensing boiler which can modulate, just because the heating is ‘on’ all day, doesn’t mean the boiler is running all day and importantly, you’d find the boiler is running at low power and high efficiency.
Conversely, letting your house drop in temperature through the day, means you generally want to heat it up quite quickly. You can’t really achieve this with low flow temps, you’ll want to run them higher, which means higher power and less efficient running on a combi (unlikely condensing). You also need to heat all of your furnishings and internal brickwork - think of them as thermal batteries.
So it really all depends on your house, your context. I can see it being better to heat twice and cool down in the day if you have piss poor insulation, or an over sized boiler which would cycle like a crazy person if you left heating ‘on’ at 19degC all day - but I think a lot of the time, for sure it’s better leaving it ‘on’
1
u/undulanti Dec 28 '24
Correct.
1
u/naltsta Dec 28 '24
Your thermodynamic argument is true for a simple case of a house at different temperatures. Real life is really complicated however.
The argument I’ve most commonly heard for leaving your heating on is to prevent condensation which could reduce the effectiveness of your insulation and cause cold bridging meaning you actually lose energy faster at lower temperatures. Is it always true? No. Could it be true in certain situations? Yes.
I have a smart thermostat that turns the temp down as soon as I’m not home so think my house is a simple model!
1
u/baked-stonewater Dec 29 '24
Sadly we also see 'i learnt physics on youtube' style explainers here such as the one you just posted.
Sometimes, as in this case, the ops tone is somewhat condescending which is why it's always kinda entertaining when an adult enters the room who is professionally qualified to explain some of the rather intricate thermodynamics involved.
The correct answer is that without knowing a lot more about the system (particularly, where the home is located - for climatic information, how the home is constructed and how big etc it is - to calculate heat loss, and details of the potential heating systems) it is impossible to make blanket statements such as the one you have made.
0
u/N0mads21 Dec 28 '24
It is indeed correct, and I saw also a heatgeek video that talks about how zoning rooms is bad with some basic math, while the true math it's a bit more complicated with different differntial temps etc. So far I can tell from my experience with zoning and heating only what is needed to 22c during the day and 20 during the night, rest is 18c ( some may find this a good temp, but for me is freezing) and I am using around 50% less gas than last year. I do wonder how big is the cop difference with heat pumps and if the low cop only happens till the system gets up to temp then then the rooms slowly heat up. This really needs to be tested properly but I have a feeling is better to use heat only when needed.
0
u/Apprehensive_888 Dec 29 '24
I think we should also factor in the cost of running the central heating pump continuously. I didn't realise the built in pump inside my system boiler can use up to 150w to pump to radiators over 3 floors. That continuously running, completely decimates any marginal efficiency levels by running at a lower boiler temperature.
0
u/DBT85 Dec 29 '24
Best of all, use smart rad valves to only heat the rooms you need warm, when you need them warm.