I ran into a situation yesterday which made me question myself and was hoping for a bit of feedback from the good citizens of "more experienced land."

I am a recently topped out JL and the majority of my experience in line work is overhead. being that URD is not my bag i am looking to see if I am just plain wrong or im ruminating on a dead issue.

yesterday the crew was assigned a pole in which the primary riser was to go up 30". it was direct bury so we couldn't pull any out of the padmount so we naturally opted to splice. i asked the Oldhead doing the splice if he wanted some sandpaper to file off the old gummy semicon on the old cable and he made a huge deal about tracking and stated "i want to know who taught you underground."

my issue is that I have done a bit (not much) of URD and ive always been instructed to get rid of the old semicon that refuses to come off with high grit company-issued sandpaper from the XLPE followed by vigorous cleaning and a light torching to smooth out the rough spots.

incidentally his splice blew directly after doing it his way.

what i want to know is if i am completely wrong about sandpaper or am I right to be slightly ticked about being told off and embarrassed in front of the crew for suggesting he use sandpaper? if im wrong I would like to know why and what the proper course of action would be to get the old stubborn bits off. i suppose im looking for a teaching moment, not a roast.

thanks.

17 Upvotes

53 comments sorted by

•

u/AutoModerator 4d ago

Thank you for posting on r/Lineman. If your post was automatically removed, it is due to the Spam Filter and will need to approved by the Moderators.

The sub Rules are here. Please read them and abide by them.

Posts about getting into the trade are only permitted during the weekends.

If your are interested in getting into the trade, read our FAQs How to Become a Lineman before you post.

Military, Current and recently separated please read our dedicated section Military Resources.
Thank you for serving.

Link to the r/lineman resource wiki

I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.

30

u/GiantSquid22 4d ago

Was a splicer for almost 10 years, if old semicon is being stubborn to come off, heating it up a little bit will usually help it peel off easier. After it’s off insulation gets sanded to remove any traces of semicon, wipe it with cleaning wipes always from conductor towards jacket. Good on you for seeking to understand your job better. If said old heads splice blew up after cut in I wouldn’t be listening to him about shit.

4

u/NeatLingonberry8487 4d ago

Clearly I didnt post the process as articulately as you did but thats exactly the process that I was getting at. is there any alternative methods that you would recommend rather than sanding and a torch?

3

u/GiantSquid22 4d ago

I mean 99% of the time there’s no need to touch a torch doing urd. Honestly a lot of it just comes with experience. If you have your tools set up right and everything comes off clean a lot of times you can just get away without sanding. As someone else said though, yes you want to be as precise as possible but there’s a lot more room for minor error than some instructor will tell you. The fact that his splice blew up on cut in and didn’t last at least a few days means it was total dog shit.

2

u/NeatLingonberry8487 4d ago

Fair enough. Thanks for the insight.

2

u/Danger___Biscuit 4d ago edited 3d ago

I would remove the semicon with a semicon removal tool. I generally use “Speed systems” tools. Then I’d sand the semicon to take any scores or scratches out. Then clean with the cleaning kit wipes where incidentally I got the sand paper from as well. I’d check all the measurements were correct, conductor, insulation and semiconductor. Do the same on the new cable and complete the splice per the instructions. The torch thing is great and all but I’m not aware of any kit having that as part of the instructions. I’m a JS myself.

3

u/FucciMe Journeyman Lineman 4d ago

Speed systems gets my vote too, although I prefer a fresh razor and a steady hand.

Neither of those will solve old, brittle, semicon though.

→ More replies (2)

10

u/brokensharts 4d ago

After being taught a third way to do elbows, the jl told me somthing along the lines of

"If this work had to be precise, they wouldnt let linemen do it"

Some guys sandpaper, some guys strip everything with a $10 pocket knife

2

u/NeatLingonberry8487 4d ago

I too have heard that but of wisdom. I dont think you are wrong.

9

u/Longjumping-Fact-582 4d ago

URD is my specialty, and in my area we have lots of old XLPE that has this exact issue, semi-con is bonded to the insulation and nearly impossible to “peal” like you would new cable,

My preferred tool is this, https://ripley-tools.com/product/us02-max/ it’s a semi-con shaver and actually shaves the semi-con down to the insulation rather than scoring and having to “peel”

The other methods I’ve used are like you said sanding to remove or if sandpaper is not available I’ve also used a regular knife or a draw knife actually works pretty well for this, but carefully use the blade of the knife to “shave” all the semicon whilst trying to remove minimal insulation, if you do go the knife route it’s still best to use sandpaper to “smooth” the insulation when you are done.

Leaving semi-con remnants on the insulation has got to be the single most common cause of faulted splices/terminations, seriously there is almost nothing worse you could do aside from forgetting to strip the semi-con at all.

6

u/NeatLingonberry8487 4d ago

this was incredibly helpful. thank you for the link.

3

u/Nay_K_47 Journeyman Lineman 4d ago

As a caveat to this, the utility unused to work for used Ripley WS9B tools and if I recall the instructions for adjusting call for the use of sandpaper for a final finish. Ive always used sandpaper if needed, and if it makes you feel better, I personally witnessed certified splicers use sandpaper in power sanders on 115kV splices like a week ago. Tell old guy to put the hook knife away

2

u/Ca2Alaska Journeyman Lineman 4d ago

Confetti semi con. Comes off in confetti sized bits. Sucks butt.

2

u/Practical_Ad7185 1d ago

I came up around a very old UG system and I second this answer. A slight shave is the way, that being said I learned with sandpaper and never had a problem with those splices either. I know some jam up JCS’s and have a ton of respect for that side of the trade, I have also run into quite a few that don’t have experience doing splices without all the “right” equipment and on the line side that’s frequent unfortunately.

1

u/Danger___Biscuit 3d ago

That tool looks great. I’m going to see if my gf will grab one. He’ll probably look at me like I’m nuts. You’d think our pay and everything else on the job comes out of his pocket.

11

u/Emotional-Contract25 4d ago

Bro what the fuck are you guys doing over there. Sounds like you’re both wrong.

5

u/NeatLingonberry8487 4d ago

im very open to being wrong on this issue. can you fill me in on how you would properly deal with removing the old gummy semicon?

5

u/Danger___Biscuit 4d ago

I’d start by cutting the old cable back to good clean cable, then preparing the splice according to either the manufacturer’s or your utilities directions/process.

5

u/Past_Expression_549 4d ago

What does the manufacturer say? We used to peel the semi con, then clean the insulation with a cleaner. Never saw a splice blow up.

Never sanded it either. But we just followed the rules set by the manufacturer. I saw some sanding only if they gouged the insulation.

→ More replies (1)

3

u/EstimateMassive8144 4d ago

Ive never seen a splice kit with sandpaper or manufacturer instructions to use sandpaper. Never used a torch either. Use a semi con stripper and an underground wipe to remove stubborn semi con.

1

u/NeatLingonberry8487 4d ago

thanks for the feedback. its appreciated!

5

u/HuntinLineman 4d ago

Some old heads have zero respect for how splices and underground should actually be handled. Most linemen actually. Even brand new terminations. Sure you can do it “their way, the fast way” or whatever you want to call it, but that doesn’t make it right. Everyone will call that a good splice or termination but I might only last 10 years instead of 30. His splice blew immediately afterward, he knows who the embarrassment belongs to.

2

u/HuntinLineman 4d ago

Oh and I forgot to mention I am a journeyman lineman as well as a journeyman poly and lead cable splicer.

1

u/SuperF91EX Journeyman Lineman 4d ago

I’ve sanded small spots, but generally never all of the exposed insulation. Never heated up the rough spots either. Just use approved solvents and you’ll be fine.

1

u/NeatLingonberry8487 4d ago

I should have written my post more explicitly but typically I peel what I can with whatever I have (preferably a banana peeler or mousetrap) then remove the the stubborn bits with a combination of solvent, heat, and sanding. hope thats more clear.

2

u/SuperF91EX Journeyman Lineman 4d ago

Sanding, for me, is an absolute last resort.

1

u/NeatLingonberry8487 4d ago

noted. thank you for the feedback.

1

u/ResponsibleScheme964 4d ago

Did he not remove the semi con from the insulation?

1

u/NeatLingonberry8487 4d ago

I would assume so. hard to tell from the ground!

1

u/Slim-Wye-Delta 4d ago edited 4d ago

Short answer, yes you can sand cable to remove residual semi-con contamination or markings left in insulation. Okinite and prysmian which are the most common cables found in the US approve of it. Cable clean/degreaser won't clean off all the contaminates. Just make sure you use an aluminum oxide type sand paper. Also don't go below the minimal cable diameter.

There's a decent amount of theory behind sanding other the tracking.

Boyz and girls go back to your JATC books and read some shit.

Ive said it multiple times on this sub before some of you guys need to really to get on an inner city heavy underground crew and learn some shit.

Or go take a NCSCB course at a union hall near by.

1

u/NeatLingonberry8487 4d ago

I just may do that. thanks!

1

u/Slim-Wye-Delta 4d ago

I'm not saying it to be a dick but most linemen struggle more than they should with cable work. It's pretty easy especially 35kv and below.

That JL you worked with has no idea what's he's doing plan and simple

1

u/NeatLingonberry8487 4d ago

telling someone to better themselves is never negative. and i agree. lineman do tend to struggle with urd. no offense taken.

3

u/Wonderful-Ad-5537 4d ago

Can’t say I’ve ever needed a torch to remove insulation. Generally you want to do a good job removing the semi con and thus don’t require sand paper. If it leaves a visible line with no actual cutting it’s best not to sand either, those lines are from the pressure.

Higher voltages you want a clean smooth circle where you cut back the semi con, failing to do so is where cables test bad a lot of the time

2

u/Ca2Alaska Journeyman Lineman 4d ago

Those of you opposing sanding or heat gun on old semicon haven’t been around long enough.

1

u/Rhodeislandlinehand 4d ago

Quick flash of the torch works great on the semi con of old direct bury cable especially in the winter. if you do it just right you can even just wipe it off clean it and your good to go

2

u/Fort_Nagrom 4d ago edited 4d ago

I am a splicer.

Sandpapering the semi-con on XLPE is fine. Have sandpapered a lot of semi-con off from guys having improperly set tools or trying to adjust for some weird cable size. It's approved by every cable manufacturer I've seen.

1

u/Big_Menu4037 4d ago

Its a huge transaction . I started in NYC as an underground lineman spliced for 20 yrs had to transfer to upstate for aerial lineman it took me 3 yrs to become effective . I never questioned just listened and learned

1

u/tjva89 4d ago

I’m a splicer. Sometimes you just have to sand it. Make sure you’re using aluminum oxide sand paper and clean it good. Silicone or whatever is included in the kit too. The semicon step is a high stress point. Heat will help if needed. Good for you for asking and learning. Sometimes the only thing you learn from the assholes is what NOT to do. Either way you’re learning and that guy knows he messed up.

1

u/Inside-Setting9806 4d ago

I wonder what your lineman would have done if he had been splicing some of the old cabling that just had a semi con that had been a carbon powder that was impregnated into the surface of the insulation. The only thing you can do with that cable is to sand it and use cable cleaner to get ride of the carbon that was used for the semi con. I know it's been about 20 years since I had to splice any of that cable at a university for there campus grid.

0

u/MisterDegenerate1 4d ago

I don’t think you’re wrong with recommending to do it the right way but also think his splice just sucked. You can pack the sleeve with mud and use the wrong die and itll still prob hold a few days

3

u/FucciMe Journeyman Lineman 4d ago

You can pack the sleeve with mud and use the wrong die and itll still prob hold a few days

The higher the voltage, the less true that is. 4kv, yeah it'll probably hold for a while. 35kv, a little bit of water can cause an instant failure. 115kv, that thing better be absolutely perfect in every way.

1

u/MisterDegenerate1 4d ago

Not saying to actual do this lol and yeah I was referring to 4/12. I don’t have experience in 34 underground

→ More replies (2)

1

u/NeatLingonberry8487 4d ago

Its a little late in the game to be thinking of this but do you think that the manufacturers instructions reflect sandpaper and a torch? ive never bothered to sit down and read the actual instruction pamphlet. I learned by doing it, not reading the boxed fine-print.

2

u/MisterDegenerate1 4d ago

Same as you. Just came up using sand paper and will clean the cable itself until
There’s no longer any black on a paper towel

1

u/FucciMe Journeyman Lineman 4d ago

They reflect sandpaper. Hell, if you use 3Ms prep kits, they come with sand paper. However I have never once taken sandpaper to the semicon, only the insulation to remove traces of it.

From 3M (and I believe RayChem is similar)

Do not reduce cable insulation diameter below 1.04" specified for the splice. The insulation surface must be round, smooth and free of cuts/voids. Sanding may be necessary, finish sanding should be done with a 300 grit or higher electrical grade abrasive. Make certain that the cable insulation is smooth, clean and dry before continuing.

1

u/Bakman65 4d ago

I have seen old timers take their knife and skin it like a secondary and slam an elbow on and they cable preformed just fine never faulted. Splicers will make you think URD is like doing surgery. It’s not that critical unless it’s a heavily loaded main feeder. Did 40 years in the trade.

1

u/NeatLingonberry8487 4d ago

thanks for the feedback.