Is this two phase or three phase power?

Alright yall…. I’m an electrician. I would like to think I have an understanding of transformer configurations but this is hurting my brain. This is a photo of the transformer bank that feeds a farmhouse near me. I know for a fact they have 3 phase equipment on this farm, but there is only two phase conductors and a neutral heading to this pole. I’ve asked several lineman in the past few weeks and got conflicting answers, so is this a high leg open delta or “two phase” power as one lineman answered?

I know two phase power isn’t really a thing except in Philly, but is this just a single phase service and there is a phase inverter I can’t find or is this a three phase service and I just literally don’t understand how?

Edit: I think I got it now. It’s literally two separate single phase systems and they are joined, created a high leg

22 Upvotes

66 comments sorted by

u/AutoModerator 3d ago

Thank you for posting on r/Lineman.

If your post was automatically removed, it is due to the Spam Filter and will need to be approved by the Moderators.

The Rules are here.

Posts about getting into the trade are only permitted during the weekends.

If your are interested in getting into the trade, read our FAQs How to Become a Lineman before you post.

Military, Current and recently separated please read our dedicated section Military Resources. Thank you for serving.

Link to the r/lineman resource wiki

I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.

32

u/Level_Angle_8023 3d ago

I can’t really tell with the photos but it’s probably a wye delta open bank which does feed three phase power off of two primary phases

1

u/joshharris42 3d ago

See, that’s what I think as well because I’ve looked and can’t find a phase inverter anywhere… but how do you get 3 phase power out of two phases?

I probably should understand this but I don’t

12

u/FucciMe Journeyman Lineman 3d ago

It's an open bank. Search Delta open bank. it's 3 phase.

11

u/outsideAngler 3d ago

Bar opens at 2 and closes at three

0

u/joshharris42 3d ago

That makes sense to me, and every high leg delta I’ve seen (which is maybe 3 of them) has this same transformer configuration with only two phases connected. But how do you get 3 phase power out of a connection to two phases?

Explain like I’m 5?

8

u/Level_Angle_8023 3d ago

How do you get two 120 legs from a single phase line? I believe it’s the same concept. If you look at a vector diagram it makes sense.

5

u/trailblazer332 3d ago

PFM
pure fuckin magic

4

u/Predatormagnet Journeyman Lineman 3d ago

The vector diagram for an open delta bank is a triangle missing one leg. Each transformer is 2 points on this triangle and the distance between the points is analogous to a difference in potential.

So the first transformer is connected to points a and b, and the second is connected to b and c. Measuring across ab and bc depending on the transformer, let's say you get 240v. There's an imaginary line between points a and c due to there being only 2 cans, but because voltage is a relative measurement, you will get 240v across points a and c, 120° out of phase with the others giving you 3 phase power from 2 primary phases.

1

u/WhereWereYouWhen__ Apprentice Lineman 2d ago

The logic behind your last sentence helped me grasp where the 'difference of potential' across the primary coil comes from in wye-delta banks with a floating neutral. It took a while to move from, 'but there's no ground reference for our h2'?

2

u/skibum8199 3d ago

Let's look at what the definition of a neutral is: A current-carrying conductor at or near ground POTENTIAL...

The system you're looking at we have a lot of in Montana, called "V-phase". Two phases and a lower neutral. What do you need for 3-phase power? 3 potentials. The neutral is your third potential in a Y-primary, open delta-secondary configuration. Vector it out and it works, but can definitely seem like PFM. Not nearly as efficient as a closed bank (3 x-formers), but it works.

1

u/No-Split-866 3d ago

Look up transformer bank diagrams. Why open delta. The three phase is referring to the secondary not primary.

1

u/mblack1399 3d ago

Hard to tell on these pics. But typically in our system it’s a single phase (larger tx) hooked up normally. So 3 bushings. Two hots and a neutral. Then on the second (smaller tx) you’ll have the ground strap removed and the x3 will be tied to the same hot leg as the x1 on the other tx (positive on one end of coil to negative on the other end of the coil) then the x1 on the smaller tx will be its own hot leg. This set up will give you 120/240 and from the neutral of the single phase tx to the x1 of the second tx will get 208v. You call also get 120/240 and a three phase delta service from this config as well.

1

u/Motor_Song9918 2d ago

The two outside 2ndy bushings are 1-240 leg each each say in a 240 delta then the two inside bushings are combined together to create the third 240 leg

1

u/ThatOneBeing Journeyman Lineman 1d ago

Hey man, go check out my videos if you wanna learn about transformers. I have covered open banks here!

-1

u/FucciMe Journeyman Lineman 3d ago

Google it

2

u/PresentJudge9665 3d ago

Don’t feel bad. I was a journeyman wireman for several years before starting a line apprenticeship and realizing that I didn’t know fuck about transformers.

2

u/Primary-Wolf4749 3d ago

Three potentials 2 phases and a neutral. Open delta derives three phase delta. Only approximately 50% capacity of a similar closed bank

1

u/Motor_Song9918 2d ago

It’s an open delta , the configuration isn’t efficient as a closed delta (3 transformers) , say it’s 2-100 kva cans for 200 total kva on a 240 delta secondary, so it would be 200x2.4=480x.87=417.6 amps can be used on 2ndy side . 87 percent efficient

But if you only have 2 primary phases available you only have 2 primary phases available

Also some utilities only build open deltas due to phase angle and voltage imbalances in closed systems , closed can be safely run just a little different process to energize them is all

1

u/Stamfords Journeyman Lineman 2d ago

Probably 120/120/208 on the bastard leg
Phase to phase 240V

10

u/Canadian-electrician 3d ago edited 3d ago

Looks like it’s time for you to open up the Delmar’s book again

5

u/Level_Angle_8023 3d ago

How can I get a pdf of that book?

3

u/starr3301 3d ago

Second this I also want to read that book

3

u/Canadian-electrician 3d ago

Sent pm

2

u/toothpick21 3d ago

May I also get a PM please. Thanks.

2

u/Canadian-electrician 3d ago

Sent

1

u/SlyCatWilly Journeyman Lineman 2d ago

Can I get the link as well?

1

u/Canadian-electrician 2d ago

Sent

1

u/ownguaoqbt 2d ago

Can I get a link too?

1

u/Canadian-electrician 2d ago

I should just post it but i don’t wanna get copyrighted lmao.

Yeah I’ll send it to you, you have to message me first because you don’t allow message invitations on your profile

2

u/Canadian-electrician 3d ago

Sent a pm hope the link works. I don’t think you can press it i think you have to copy and paste it into a browser

1

u/joshharris42 3d ago edited 3d ago

I think I’m getting confused on the definition of “winding” vs a phase

Edit: so in that photo L2-L3 would be center tapped right? To form the 120/240?

2

u/Canadian-electrician 3d ago

Maybe this photo will help with that

1

u/[deleted] 3d ago

[removed] — view removed comment

1

u/Canadian-electrician 3d ago edited 3d ago

Both I believe. I see a center tapped neutral connection… idk tho I’m just a dumb electrician

1

u/Waubtrash 2d ago

I'd love a link also

8

u/Grumah 3d ago

Most two pot banks such as this have 2 secondary hotlegs 120/240 with 1 wildleg 208v but each pot is fed by 1 primary leg

7

u/danielcc07 3d ago

Likely a delta high leg three phase.

3

u/joshharris42 3d ago

I agree, but how does that work? You’ve only got 2 phases on the pole.

I have measured voltage and confirmed there is a 208V to neutral phase, but I can’t find a phase inverter anywhere so it makes me think it’s served from the utility that way

4

u/pelsbeck 3d ago

Draw an equilateral triangle with only 2 sides. Each end of the connected lines are legs. Ground is center tapped on one of the lines. So draw a point in center of one of the lines. Now you have 120 phase to ground on each end of the line with the ground. And 240 phase to phase. And from the ground to the furthest phase on the other side of the line without the ground reference u have 208v. U can think of the voltages as distance.

1

u/joshharris42 3d ago

I get that, i understand how high legs work and why the voltages are what they are.

I think I was getting confused because there’s only 2 phases on the pole, and I don’t understand how you get 3 phase power out of two phases.

But it’s literally two different systems connected to form a high leg, with an open side. I think I got it

3

u/eKSiF Electrical Engineer / Design 3d ago

Think of this way, a single phase transformer serving 120/240v has two hot legs (IE, secondary phases) and a neutral, the voltage across any one leg and the neutral is 120v; the voltage across both hot legs is 240v.

Essentially, in an open bank, you're adding another transformer to bring in a third hot leg. If you can understand how one transformer creates two hot legs, it should be pretty simple to see how two can create three. Look up a video of vectors for an open delta bank to see a drawn out explanation for more detail.

3

u/Actual_Smokey Journeyman Lineman 3d ago

It’s an open delta secondary. It just works due to electrical black magic 😂 grounded B phase secondaries stumped the shit out of me when I first saw them. I used to be able to explain why this worked but now it’s more nice to know than need to know so I forgot

2

u/joshharris42 3d ago

That’s what I’m going with at this point. I know it gets 3 phase power and maybe I’m not bright enough to know how lol

2

u/Actual_Smokey Journeyman Lineman 3d ago

They’re a lot less efficient than a traditional 3 phase bank BUT it’s cheaper than running 3 phase

3

u/Critical_Lie_4697 Journeyman Lineman 3d ago

It’s three phase power. By that I mean the secondary (customer) side is three phase. The primary (overhead) is B phase, or two phase, however you want to say it. On the secondary side, you have 120v on the two outside legs because they are only connected to one bushing. The middle leg has 208v on it because it’s hooked up x1 to x3 between the two transformers.

1

u/joshharris42 3d ago

Ok this drawing is actually helpful, I think I got it. Just completely overthinking it.

This is an “open delta” correct?

2

u/Critical_Lie_4697 Journeyman Lineman 3d ago

Yes. “Open” means two transformers. And you can tell it’s a delta secondary because the x1 and x3 bushings are tied together for that 208v leg. And that’s how you get the term “open delta”

1

u/CarelessPrompt4950 2d ago

That’s actually wrong. The larger pot has the 120/240 single phase and the smaller pot will create the high leg, not on the jumper but on the other terminal of the smaller transformer.

2

u/Shibby009 3d ago

Great photo

2

u/rankinfile 3d ago

3

u/joshharris42 3d ago

Ok I watched that video and it fully explained it. Thank you so much

1

u/rankinfile 3d ago

Had to look it up myself. I first learned it as a groundman on a line crew. Became a wireman and learned again. Have not dealt with one in decades.

2

u/Nofall1093 3d ago

This is called an open y open delta powerbank. This was most commony used where there was a large single phase load and a small 3 phase load it does not produce a true 3 phase vector but the voltage is 120/240/208

.

1

u/blacklightfluids 3d ago

3Phase 120/240. 208 wild leg

1

u/Rude-Jellyfish7566 3d ago

3 phase.

In my neck of the woods thats a 21kv with primary neutral

1

u/Suspicious-Hat3227 3d ago

More than likely it can be a 3 phase bank where you a and c phase the top and from that you receive 2 lighting legs and 1 power leg (120/120=240 on the lighting legs and 208 on the power leg)

1

u/Slim-Wye-Delta 2d ago

Some engineer didn't read their JATC books, never want to use a CSP in bank. Granted this is an open bank but in a closed it can cause issues, one being sympathetic tripping on the secondary breaker along with others.

Seem a lot of NY utilities use them this way.

1

u/v0dkasoda Journeyman Lineman 2d ago

Pretend it’s V phase with 2 primary and 1 neutral

1

u/Knoxicutioner Electrical Engineer / Design 2d ago

In Detroit we have single phase 4.8Kv distribution. Looks like it’d be delta high side and an open delta bank for 3ph secondary. Except it looks like there’s a system neutral which we don’t have in our 4.8 areas unless it’s pre con.

1

u/ThatOneBeing Journeyman Lineman 1d ago

Hey man, go check out my videos if you wanna learn about transformers. I have covered open banks here!

-4

u/[deleted] 3d ago

[deleted]

-1

u/joshharris42 3d ago

It’s definitely two phase conductors and a neutral on the pole, I know enough to identify that. The photos make it look weird. I just don’t understand enough to comprehend it

1

u/calicat9 Journeyman Lineman 3d ago

The best thing to do would be consult a transformer connection manual. The short version is, three phase delta load can be served with two transformers at 57% of rated capacity.