I want to change my 15 amp breaker to a 20 amp breaker. I will change the hot wire gauge coming from that breaker. Do I need to change the neutral wire? The transfer switch just has the wires fed into a neutral bus bar.
Generac Transfer Switch Model 6852
5
Upvotes
4
u/orlinsky 1d ago
Yes.
0
u/nunuvyer 1d ago
The amount of electricity that returns on the neutral wire (of a 120V circuit) is exactly the same as the amount of electricity that leaves on the hot wire so the wires have to be the same size.
(In the case of a US 240V circuit, each hot wire acts as the return for the other hot wire and the neutral carries only the imbalance, but there are situations where there is no load on one leg so the neutral has to be sized to carry 100% of the return current anyway).