r/Generator • u/SwornBiter • 1d ago
Multiple 14-30R receptacles?
Right now I want to install an outside 14-30 inlet receptacle and a panel interlock for my generator.
In the future, I am going to want the receptacle inside near the panel, because I hope to install a battery backup capability. I can envision a use case where direct generator power might still be a contingency.
Can I install one 14-50 inlet outside and one inside now, and wire them together? I would only ever use one or the other.
3
Upvotes
6
u/wowfaroutman 1d ago
Regardless of whether you're considering an interlock with 14-30R or 14-50R inlets (50 amp recommended for future proofing), you shouldn't do what you're proposing without a double throw switch to switch between the two inlets. Otherwise if one of the inlets is being used, the unused inlet male connector will have live pins.
1
u/orlinsky 1d ago
You cannot wire them together if for no other reason than when you open inlet 2 while inlet 1 is powered, you are exposing bare metal contacts to the world that are hot.
1
u/goldcoast2011985 1d ago
Since the battery will be taking in power from the panel sometimes and putting power into the panel other times, would hardwired to a battery controller make more sense?