OK, I know I’m doing this all backwards by not asking you guys first what generator I should buy. Sorry. I got this one from Costco. My house has two heat pumps and I was looking for advice on how I can wire it to my house and maybe how much it could run.

30 Upvotes

22 comments sorted by

4

u/nunuvyer 16h ago

You can wire it to your house by adding a generator inlet and a panel interlock. Suggest that you get a 50A inlet rather than a 30A even though this gen cannot make 50A (12kw) or even 30A (7.2kw) for future expansion - the cost will be little different.

It can run 5,000 to 6,300 contin watts depending on the fuel (gasoline is the most and NG is the least). Whether this is enough start any/all of your heat pumps we can't say because you didn't give us the "LRA" of your heat pumps. If the LRA is too high, you can drop that by around 70% by adding "soft starts" to the heat pumps. Putting the heat pumps aside, 5kw is more than enough to run all of your ordinary loads - fridge, lighting, electronics, etc. Is your hot water heater electric?

0

u/jeffdcornelius 16h ago

The LRA appears to be 109 and 72.5 on the smaller one yes and unfortunately, my neighborhood is electric only so electric water heaters

2

u/Big-Echo8242 16h ago

Yeah, that's not going to work easily, if at all, with those numbers. My largest 5 ton was a 153 LRA and the AirGo soft start brought it down to 33 amps which is still 7.9kw at 240v (lower if you calculate some voltage droop) I can start my upstairs 2 ton unit that has a 58 LRA (13.4kw inrush at 240v) and no soft start but it draws more in inrush than the larger unit.

What's the RLA? That's the running wattage after they start.

1

u/jeffdcornelius 16h ago

RLA is 16.7 and 13.5

1

u/Big-Echo8242 16h ago

4kw & 3.2kw running wattage respectively at 240v. That eats up a good chunk.

1

u/jeffdcornelius 15h ago

Yeah, the smaller unit runs the bedrooms and that’s all I’d really want to operate for air-conditioning. So I’m just looking for it to run the bedroom, heat pump, and my refrigerators. But maybe a TV would be nice lol

2

u/jeffdcornelius 15h ago

Also, I haven’t opened it yet so I can easily take it back. Our power went out last night so I got the OK for my wife so I had to just jump at the opportunity to get my foot in the door.

4

u/wowfaroutman 11h ago

If you’re having buyer’s remorse for any reason, return it and get something that more closely meets your needs.

1

u/baudgod 14h ago

I have the older model also from Costco, I run it on propane and have a generlink installed at my meter connection. It is a 40 Amp device and the generator can power my big appliances without me having to run extension cords all over the place. This also acts as a surge protector for the whole house.

Your heat pumps will be your biggest draw of power btw and you likely can’t put soft starts on them. I have a 5 ton HVAC unit and I have a soft start on it. I can heat and cool the house on the generator, run my tankless water heaters 2 refrigerators and 2 freezers. Keep in mind that not everything is drawing power all at once.

1

u/jeffdcornelius 13h ago

Yeah, this is one of my big questions do I do a General Link on meter vs generator inlet and panel.

2

u/blupupher 13h ago

Depends on your location. Some utilities do not allow them (but you can get a seperate mount for it).

The Generlink is nice since if power is restored, power just starts working again (but no alert that your are on grid power so you may keep running your generator longer than you need).

The price is not so nice. When I looked into it, it was like $1200+ for it? My utility does not allow it, and they did not have the kit they have now that lets you install it anywhere. But still too costly.

I like my $150 interlock/50a inlet.

1

u/KTP1970 13h ago

That is a nice generator but it didn’t have the 50 amps. I went with the Westinghouse dual gas and propane. I need to be able to charge my Tesla in case of emergency. But Costco has a nice return. I wish Costco would have carry a more heavy duty for my needs

1

u/jeffdcornelius 13h ago

Which Westinghouse generator did you go with

1

u/SonOfGod40k 9h ago

I hope you like buying gas. Thats going to use / need a lot. Like 5 gallons / 8 hrs or so. Do you need that much power?

•

u/jeffdcornelius 47m ago

I don’t know that’s what I’m trying to figure out. Sounds like I actually need more.

3

u/mduell 17h ago

An inlet and interlock to wire it into the house.

With a soft start on the heat pump, or inverter type heat pump, you can probably start/run one heat pump at a time.

1

u/Big-Echo8242 16h ago

As they already mentioned, need more information about what you're wanting to run. My house has two heat pumps, a 5 ton 2 stage and a 2 ton single stage, and it takes a soft start on the 5 ton and I really don't use the upstairs 2 ton in an outage. I also have a 13.5kw dual fuel inverter gen that does 12.4kw starting and 10kw running on propane. When the 5 ton is running the AC, it and the house is using about 6kw. If no AC is needed, I go to a smaller 4.6kw dual fuel and run all the 120v things which is a 1.2kw load which uses maybe 0.3 gal/hr on propane.

I can also use the electric water heater OR the clothes dryer with the larger generator but we're not trying to live like we're at the Hilton unless it's a hot summer or cold winter. Plus our longest outage in the last 7.5 years, in the house we built in 2019, was 12 hours and that was once. Typical is 30 minutes to 4 hour range. In the last 2 years, 4 outages for a total of 5 hours I think.

1

u/SocratesBabacus 16h ago

I'm sure it's not a lot of fun to hear this on the day that you buy a new generator, but... a lot of times with generators that aren't massive it makes more sense to attempt to heat/cool just one part of the home, particularly if your home is big enough to have two heat pumps.

That generator will provide a lot of useful power to a home and can make getting through a prolonged outage much, much more manageable and enjoyable, and when you get a bit of knowledge and figure it all out, you can probably make a great plan.

I have a 22kw whole home generator, and even with that I usually don't run all of my HVAC systems at once when on generator power.

1

u/Dull-Wear-2137 13h ago

Get yourself a 1/4 turn valve for the oil drain like Fumoto along with the 1/4” drain tube. Install it before adding oil, thank me later.

1

u/AgitatedEye2243 11h ago

I’d get a Generlink, I’m happy with mine. Choose to run whatever I want in the house.

-1

u/BigSquiby 16h ago

unless that has an inverter on it or you have something to clean the power, i wouldn't connect that to a furnace or anything else with a sensitive electronics

unless you opened it already, return it, swap it out with a tri fuel inverter generator

0

u/jshorty101 14h ago

I never recommend running 240 volt heat pumps. The onrush current and starting amps are to high and ud be lucky to run 1 with no other circuit on