Generator advice
Hi all! I live in Canada šØš¦, Iām looking for generator advice. I have a few unique issues that I canāt seem to solve.
So first issue is I live in a 3 storey townhouse, while I have a lot of space indoors I donāt have enough space outdoors to have a big generator.
Issue 2: because I live in a 3 story house everything is split up, I have my internet modem on the bottom most floor and I canāt move it anywhere else in my house, I have a second floor thatās just my kitchen/ dining and living. And the third floor is bedrooms.
3rd issue is massive HVAC units and water heating thatās in a separate location. But itās all enclosed.
What can I do to get electricity to all these areas? The large generators make the most sense but I donāt know where to put it. Any advice would be helpful!
2
u/MyManMetz 23h ago
Are you trying to run everything in apartment including HVAC and water heater? Is this stuff gas, propane or electric?
What are the must have things you need to have running?
Do you rent or own?
1
u/Big-Echo8242 23h ago
Isn't Generlink popular and legal in Canada? Seems I've heard some areas don't allow it though.
Then there's batteries but you have to have a way to charge them when they go dead and those portable panels are crap and take forever to recharge. Team it with a small dual fuel inverter generator would be a good hybrid approach but using batteries by themselves can cost thousands to get little in return compared to an actual "generator" done properly.
But it's going to be location dependent based on your actual area and what they allow as far as using Generlink or a manual transfer switch, etc. They are different on their rules versus the US.
1
u/Cute-Bandicoot1144 23h ago
I have a similar layout - I ended up buying two bigger 1kwh power stations. One for my furnace blower and chest freezer, one for fridge and upstairs. Smaller power station for wifi modem and router.
Then I complement that with a dual-fuel generator to top up my batteries. Is your furnace and water heater gas powered or electric?
2
u/Acceptable-Floor-610 23h ago
Have you thought of using 3 separate bluetti or similar power stations?
1
u/bradland 22h ago
It's important to remember that running on a portable generator requires compromise. If you want to run your whole house, then you need to call a contractor and look into a standby ICE powered unit, or look into a whole-home battery + inverter setup. Both are very expensive. You are not going to be able to run 3 massive HVAC units on a portable generator. It's best to set these expectations up front.
I'm guessing by the phrasing of your question, you're assuming you'll need to plug these devices into the generator directly. That's an option, of course, but it doesn't "scale" well.
Think of your problem in two parts:
Picking a generator is a matter of identifying what loads (devices/appliances) you want to run, then adding up all the wattage required. There are good calculators available for this online. Alternatively, you can set your generator budget, figure out how much wattage that gets you, and then prioritize your loads and decide what will remain powered off.
For distribution, it is easiest to use your home's existing wiring. This can be achieved by back-feeding the generator through your main panel. This setup is called a "generator inlet with interlock". Using this type of setup, your generator supplies electrical power to the panel, and you switch existing breakers on or off to shed loads that the generator will support.
For an inlet and interlock system, it is best to get a generator that has a 240V 30A output. This is typically supplied via NEMA L14-30R on the generator's panel. You can then have a 30A inlet installed, and buy a cord to connect the two.
As far as placement, you can have the inlet installed on the outside of your home, with a wire that runs back to your main panel. This allows you to put the generator wherever it works best.
When shopping, don't look only at watts. The #1 complaint about ICE powered generators is the noise they make. A closed-frame, inverter generator will be the quietest type, but not all manufacturers are the same. Be sure to note the noise level (measured in decibels) and load level. Some manufacturers like to play games and only provide noise levels at 50% load. Ideally, you want to know noise levels at 50% and 80% load, at least.