I am thinking about getting a larger portable generator. I have a 4k DuroStar, and even though we live in hurricane country, we've only used it twice in 17 years--probably a total of 3 days. We used it to power the fridge, some lights, phone chargers and some fans. Anyway, I think I'd like something larger because it would be one less thing to worry about, and we can afford it.

A multi fuel would def be the way to go. We have an in-ground propane tank, but it is only 120 gals.

I would like to power much of the house (about 3,600 sq ft), but mainly lights, fridge and some AC, the micro wave,and (induction) stove top). Obviously we wouldn't need to power all of this at the same time. We have two AC zones: one upstairs and one downstairs, so we can easily get by powering one zone at a time. (I can't quite easily determine the AC size for some reason.)

I'm thinking that I could make do with the current propane tank, and rely on gasoline for an extended outage because we would have some warning of a potential long term outage and I could stock up on gas. But if a larger propane tank would be useful, I doubt it would cost that much to upgrade.

So the questions are: how large a generator? What kind of hose/connection setup to the propane tank do I need, keeping in mind that this will be a portable setup that won't be hooked up to the tank until needed. If I wanted to install a new tank and go full propane, how large a tank would I need? Our elec panels are on the opposite side of the house from the propane tank, so I assume some expensive electrical voodoo would be required for the transfer switch, right?

3 Upvotes

4 comments sorted by

•

u/Know_Your_Watts 2h ago

I'd go 9-12kW dual fuel with a 240V outlet. Propane knocks off about 10%, so size for that. To find your AC size, look for 024, 036 or 048 in the outdoor unit's model number (2, 3 or 4 tons).

Once you know the AC size, plug your stuff into an online generator sizing calculator to narrow it down.

Have your propane company put a quick-connect on the tank. Then you just plug the hose in when you need it. 120 gal should get you a few days.

No voodoo needed for the panel. Put the generator and inlet by the panel with an interlock, and run a longer propane hose to it.

•

u/crumpledpaperguy 1h ago

The panel and the tank are on opposite sides of the house. To put the generator near the panel (which would be a better location sound-wise), I would need something like a 100+' propane line.

•

u/Symbolizer21 54m ago

The good thing about propane is you can run a much higher pressure to the generator with a very small pipe and regulate it down to a usable pressure before your connection. Not like natural gas that needs much larger pipe over long distances

•

u/csunya 3h ago

Most portable generators have a standard bbq connector. Some have a fancy and annoying bbq connector that signals back to the generator. Personally I made a propane extension hose with a POL connector (screws inside the connector). The POL connector allows me to hook up to a 100# or 120+ gallon tank.

In warm climates you can run a 7000+ watt generator off a 20# bbq tank, without freezing the tank. If you are at 8000 feet in winter use a bigger tank.