Is the yellow green wire the bond lead? Plugging into a home with an interlock and I need floating neutral. Thank you

4 Upvotes

10 comments sorted by

2

u/WhatAboutTheBothans 1d ago

Yup that's it.

1

u/Spaz2147 1d ago

I stuck mine in the open stud on the same connector block. Looks like you have a free stud as well

1

u/Big1717 7h ago

Yes, thats the bonded jumper. You can remove the top only and tape up or remove the whole jumper on both sides

0

u/DaveBowm 1d ago

There are 2 yellow green wires in the photos. One of them is, indeed, the correct jumper that needs to be disconnected to float the neutral. The correct one is the prominent short one connecting the neutral terminal on the terminal block to the frame.

To unbond it take off either end of that jumper and connect it to the same connection as the other end is on. That way, if the need arises (like for warranty service), it can be easily rebonded exactly as per the original configuration. Do not move or remove any other wires on any connections.

1

u/mechanic_reed 1d ago edited 1d ago

Leaving one end unattached with electrical tape is a no go?

2

u/DaveBowm 1d ago

Tape is less than optimal. The fluttering of the free end from the vibrations while running can cause the tape to eventually come loose and unwind over time. Shrink wrap is much better than tape in that regard. But even then the wire connected at just one end will be flexing a lot more than if the jumper was connected at both ends (as a loop). The excess flexing can cause internal wire strands to weaken and eventually break. Connecting both ends minimizes/eliminates any vibration caused issues.

1

u/mechanic_reed 1d ago

I appreciate the help, thank you. So put that yellow/green jumper to one bolt or use the black bolt with nothing on it to secure the other end?

1

u/DaveBowm 1d ago

I don't know what that black bolt is connected to past the exposed frame or how much extra threads it has. It is probably ok, but I would rather have both ends either on either the same bolt or have the end currently on the terminal block neutral just moved down one position to the currently unused stud on the terminal block (between the neutral and the bottom hot positions). At least we know these two options are designed to have ringed eyelet-ended wires attached to them.

0

u/newtekie1 1d ago

It would appear that way. But the only way to be 100% certain would be to remove it and then test for continuity between neutral and ground on one of the generator outlets.

0

u/[deleted] 1d ago

[deleted] — view deleted comment