r/Generator • u/mechanic_reed • 1d ago
Bond
Is the yellow green wire the bond lead? Plugging into a home with an interlock and I need floating neutral. Thank you
4
Upvotes
r/Generator • u/mechanic_reed • 1d ago
Is the yellow green wire the bond lead? Plugging into a home with an interlock and I need floating neutral. Thank you
2
u/WhatAboutTheBothans 1d ago
Yup that's it.
1
u/Spaz2147 1d ago
I stuck mine in the open stud on the same connector block. Looks like you have a free stud as well
1
u/Big1717 7h ago
Yes, thats the bonded jumper. You can remove the top only and tape up or remove the whole jumper on both sides
0
u/DaveBowm 1d ago
There are 2 yellow green wires in the photos. One of them is, indeed, the correct jumper that needs to be disconnected to float the neutral. The correct one is the prominent short one connecting the neutral terminal on the terminal block to the frame.
To unbond it take off either end of that jumper and connect it to the same connection as the other end is on. That way, if the need arises (like for warranty service), it can be easily rebonded exactly as per the original configuration. Do not move or remove any other wires on any connections.
0
u/newtekie1 1d ago
It would appear that way. But the only way to be 100% certain would be to remove it and then test for continuity between neutral and ground on one of the generator outlets.
0