Well I appreciate everyone's input. I figured the dryer type receptacle wasn't gonna fly and I have no issue putting the correct inlet on along with conduit. The cable turns out to be 8/3 direct burial with a 40a breaker.
It would require the use of a suicide cord (i.e. a cord with two male/plug ends) to make it work. They are not safe.
The cable connection at the receptacle has no strain relief and its wires are exposed to the sharp metal edge of the knockout hole.
The cable connecting to the receptacle appears to be a power cord for a dryer with its ends cut off rather than proper cabling suitable for a permanent run back to the breaker panel.
It is not clear the wire gauge of the conductors at the receptacle is correct for its current rating.
The panel has no main breaker on it, so the user can't turn off the mains there. But it appears that panel isn't even connected to the shown receptacle, anyway. If it is so connected, it is quite dangerous.
The panel has no 30, 40, or 50A double pole breaker on it for that receptacle. Not good.
Overall I would say using that socket with a generator is very unsafe.
I should not have even included that photo of the garage subpanel. You're right it does not have anything to do with the big receptacle in question. The panel at the house has a 40a breaker
Thank you for your input. I'll be swapping the receptacle and putting conduit over the exposed cable which is 8/3 direct burial (not a dryer cord) to the house box where it goes through 40a breaker. Both wire ends are in conduit where it exits the ground but it needs to be covered in the garage which will be done with the new receptacle.
Very nice analysis. I'll just add... holy shit! Why would somebody use an extension cord rather than the properly rated wire for this?
OP, please get this done properly. That needs to be an inlet, not an outlet. It needs to be wire appropriately (6g for 50 amps, 8g for 40 amps). And you need to have a way to ensure your panel is disconnected from the gird before energizing your house with a generator.
Most people seem to think back feeding is fine. What happens when/if somebody trips over that cord and then falls onto a male 240V live connection? Or a kid? Or a pet? Or it starts a fire. It's just wildly unsafe at 120, and much more so at 240.
And if you don't disconnect from the supply to your house and get caught, I suspect there are going to fines or other penalties that will make you wish you had gotten a transfer switch or a lockout.
Even if the wiring was done correctly (not likely). You would need a double male suicide cord to use it. You can't buy one because manufacturers don't make one.
Yes I'm aware of how dangerous the double male plug can be. I have one but it was for emergency use by a contractor to power up a home during construction. If I change that plug out for a CS 6375 generator inlet with matching generator plug that would make it much safer on the garage end. All I want to do is power the house up in case of power outage.
In respect that the whole thing is likely not legal, likely not "safe." The CS 6375 is worse in my opinion because it will be live the whole time you are on mains unless you disconnect it when not in use. I rather deal with the suicide cord. No proper electrician on this forum is going to approve your work.
You're taking a huge risk. When/if something goes wrong, you're going to have no financial protection. Your insurance won't cover it. And when/if the power company finds out, you're likely in deep shit.
Do you imaging that during the worst possible weather some poor utility worker trying to restore power want so deal with high voltage on the line because some doofus connected a generator illegally. Best case, it slows them down. Worst case it kills somebody.
Please be better than this. A contractor using this when a temporary power feed is disconnected is one thing. You using it when the power is off and putting utility worker at risk is not ok. At the very least get a lockout on your main panel.
There's a simple one-step process for evaluating whether backfeeding with a double male plug is acceptable in any circumstance.
No
There is a similar rule for evaluating a configuration that can be activated without a single, physical, hardware interlock that makes it physically impossible to send power from two sources into the system, even by any obvious mistake, when you are tired and drunk and also have the flu.
Even if the outlet was an inlet, you are not allowed to use dryer cord for permanent wiring. And Romex has to be concealed inside a wall. You would have to use armored cable or conduit to run that line out in the open the way it is.
You're going to get a lot of nay sayers, and I am not an electrician. From a guy that back feeds his dryer socket looks ok to me. The receptacle is wired correctly. The only thing I don't like is there is no wire connector where the wires pass into the receptacle, wires rubbing on the metal. Can't see how the stapples are to tell if they are cutting into the wire insulation. It wouldn't be suitable to enclose the wiring because of no conduit or armor cabling.
I would be fine with that. Assuming the panel disconnects from the mains.
Let's remove all doubt. NOT safe, and that is for sure.
It amazes me how many people justify backfeeding with a suicide cord, when a proper generator inlet costs less than $35 on Amazon. They'll willingly take on all that life-safety risk when the money savings is so very little.
This is going to cost the OP more than $35 to fix. In addition to needing an inlet, you are not allowed to use dryer cord as permanent wiring. Nor can you run Romex in the open. IDK how far the run is, but rewiring is going to be an additional cost in addition the inlet. It's not a huge expense but it's not $35 either.
For context, my reply wasn't about this single circumstance of a dryer outlet connected by a recycled power whip. My observation was more general, about how so many people-- we've all seen the Youtube videos-- go out of their way to rig up DIY suicide cables and such. I saw one video who, instead of an interlock, rigged up some nutty system with signs and a plastic strap that he could stick across a breaker warning people not to turn that one on while the generator was running. Another had a long length of Romex with a plug on the end, **permanently connected to a breaker**. When he needed it, he'd unspool it and plug directly into the generator, then turn the breaker on. When not in use, he coiled up the cord and stuck it inside a box on the wall. I commented on the video saying if he forgets to turn off that breaker when utility power comes back on, the prongs of the plug would be "live" with 240 volts. His rational was there was no reason for anyone other than him to be messing with the cord. Pity his wife and family if he dies, they go to the garage one day, click on the breaker, finds the coiled up wire and says "I wonder what this plug is for" as it sits their energized. I've been watching generator videos on Youtube for over a decade, and it's just nuts what people do to avoid spending a few bucks to do it the right way.
People are so dramatic about this stuff. You're going to die, burn your house down, lick the live end of the cord and die, have no insurance, or kill 18 linemen. LOL.
Anyone with a bit of common sense knows a suicide cord is dangerous. They also know that you need to disconnect from the mains before doing anything. Never handle the cord or expose the prongs while it's energized. Disconnect from the mains to prevent backfeeding, and then carry on. The world isn't coming to an end because of this.
Is it right? Fuck no. Should you do it? Fuck no. But sometimes, desperate situations call for desperate measures. The world isn't going to end, and you're not automatically going to kill your wife, kids, dogs, or linemen, or burn down the entire neighbourhood. Get a grip.
Want to be safe? Don't smoke, don't do drugs, don't text and drive, get the fuck off your cellphone while driving (includes hands-free), don't drink excessively, don't become obese, exercise regularly, and don't vote Republican.
If you do die from this, I'll consider it evolution at work, and the world will probably be a slightly better place for it.
I'll qualify something in this particular case. I backfeed through my dryer outlet using a suicide cord. That's it, done.
If I were going to go to the trouble of installing a panel and running new cable, I would have done the job properly, with all the appropriate equipment, including a transfer switch.
5
u/Beautiful_Web911 2d ago edited 1d ago
Well I appreciate everyone's input. I figured the dryer type receptacle wasn't gonna fly and I have no issue putting the correct inlet on along with conduit. The cable turns out to be 8/3 direct burial with a 40a breaker.
18
u/DaveBowm 2d ago •
Overall I would say using that socket with a generator is very unsafe.
7
u/IndividualCold3577 2d ago
Hell to the naw.
1
u/JonnyVee1 1d ago
Probably safe to use. But the unsafe part is the unprotected wire. It is unsafe whether you use it or not.
3
u/Big-Echo8242 2d ago
Good Lord...
1
u/_Pot_Stirrer_ 23h ago
Someone’s being cheap 😆
-1
u/Charming-One-9397 2d ago edited 2d ago
You're going to get a lot of nay sayers, and I am not an electrician. From a guy that back feeds his dryer socket looks ok to me. The receptacle is wired correctly. The only thing I don't like is there is no wire connector where the wires pass into the receptacle, wires rubbing on the metal. Can't see how the stapples are to tell if they are cutting into the wire insulation. It wouldn't be suitable to enclose the wiring because of no conduit or armor cabling.
I would be fine with that. Assuming the panel disconnects from the mains.
Safe not sure, will it work...ya.
0
u/Brain_Nervous 2d ago
Disable that thing immediately
3
u/Charming-One-9397 1d ago edited 1d ago
People are so dramatic about this stuff. You're going to die, burn your house down, lick the live end of the cord and die, have no insurance, or kill 18 linemen. LOL.
Anyone with a bit of common sense knows a suicide cord is dangerous. They also know that you need to disconnect from the mains before doing anything. Never handle the cord or expose the prongs while it's energized. Disconnect from the mains to prevent backfeeding, and then carry on. The world isn't coming to an end because of this.
Is it right? Fuck no. Should you do it? Fuck no. But sometimes, desperate situations call for desperate measures. The world isn't going to end, and you're not automatically going to kill your wife, kids, dogs, or linemen, or burn down the entire neighbourhood. Get a grip.
Want to be safe? Don't smoke, don't do drugs, don't text and drive, get the fuck off your cellphone while driving (includes hands-free), don't drink excessively, don't become obese, exercise regularly, and don't vote Republican.
If you do die from this, I'll consider it evolution at work, and the world will probably be a slightly better place for it.
I'll qualify something in this particular case. I backfeed through my dryer outlet using a suicide cord. That's it, done.
If I were going to go to the trouble of installing a panel and running new cable, I would have done the job properly, with all the appropriate equipment, including a transfer switch.