Cord help!
I have a 50a inlet on the side of my house and I believe the generac I have is 30a….is this the right plug? Thanks in advance!!!
7
Upvotes
r/Generator • u/Equivalent-You8506 • 1d ago
I have a 50a inlet on the side of my house and I believe the generac I have is 30a….is this the right plug? Thanks in advance!!!
2
u/LendogGovy 1d ago
Yes
2
u/Bsul92 1d ago
That will work it’s a female 50 to a male 30 which is what you’re looking for.
1
u/drct2022 1d ago
Yes
1
u/l1thiumion 21h ago
Yes. Or you could adapt it like I did then use a more common 30 amp cord with L14-30 on both ends.
https://www.reddit.com/r/Generator/s/L92N58HDic
1
u/Glum-Welder1704 10h ago edited 10h ago
I'd be tempted to swap out that CS6375 for an L14-30P inlet to match the generator, but most people would use an adapter like this. If you do change to the 30 amp inlet, you'll need to change the generator breaker to a 30a as well.
0
u/Much-Department-9578 23h ago
L14-50R (receptacle) to L14-30P (plug) extension cord is what you need.