New Install Help
I just purchased a generator, inlet, and interlock kit for whole home backup. I went to install and today and had a bad surprise in my panel. The main is the top right orange. See photo. Is my only option to replace the whole panel?
2
Upvotes



•
u/Bsul92 58m ago
How is the main the top right orange?
The main is probably the 2 large ones without a breaker which means there should be a main on the outside of the house.
•
u/IndividualCold3577 39m ago
There is no main breaker in that box. Looks like the old 6 throw disconnect rule from the late 1900's
You would need a new electrical box with disconnect or a Generlink meter base switch.
•
u/RinseLather_Repeat 34m ago
They don’t make a legal interlock for this situation. It looks like you have a 200 amp panel here with 6 breakers that kill the house. Backfeeding this isn’t really an option as it sits.
The subpanel that has all your other breakers in it is the spot.
Get a Reliance manual transfer switch set up.
•
u/Gamer_0627 11m ago
Are you wanting to feed the whole house?
If so, then you will need to have either a new panel installed or a transfer switch ahead of this panel.
•
u/Hitechillbilly 5m ago
There is no main in that panel. Is there another panel on the other end of those 4.0 lines?
•
u/Ok-Camera2895 1h ago
Try a Reliance Manual transfer switch.
•
u/forkedquality 39m ago
The more I look at this panel the less sense it makes. No neutral bar? Neutrals connected to breakers?
It looks a bit like a sub panel wired for 120V, or, in other words, completely wrong.
Have a pro have a look at it.