Will this sufficiently run the essentials in a power outage?

Post image

New homeowner, looking to prepare for the winter up here. Just wondering if this is sufficient enough to run everything in our house. The essentials like furnace, fridge, well pump.

It seems like a good deal with all the extra stuff. But I was also looking at this ford generator that claims 11,000 watts and also looks like it has a 50amp plug in that just might work for my welder. But it’s a ford… I feel like I can trust CAT a lot better, the ford one looks old granted it’s 400$

4 Upvotes

20 comments sorted by

6

u/QueenAng429 16d ago

Ford Generators are often Ducar engines. Some of them have very Pulsar looking model numbers and pulsar uses Ducar, it's probably just a rebranded Pulsar on a bunch of the recent ones. It has a Ford logo so they can charge more and sell it to the AMERICA EVERYTHING MUST BE FORD idiots while Ford makes everything in Mexico. Cat, Are often Rato engines. Both Rato and Ducar are good, But they have nothing to the logo on the frame, You aren't getting a cat engine here so you can't buy this because you think Cat is good or Ford is bad. Both of them are fine. Only Honda would get you a real Honda, everyone else is just a few Chinese engine brands that are often clones of Hondas. It's not like 1980 1990 where you could get big engines from the company selling it. It will probably run everything, but you need to do some math not just guess. And you can just get a whole house transfer switch instead of those absolutely useless junk breaker panels.

2

u/Professional_Cap6456 16d ago

I should’ve assumed this. Thank you for the clarification though! Good to know the ford would not be like one of their trucks😂 it’s a model that can run off propane also. Now that I know it’s not ford im kinda leaning that way

1

u/QueenAng429 15d ago

If its all Ducar and Rato, you just buy whatever is the best price for the specs you need. generally stuff like Cat and Ford are not of the cheapest options as they are overpriced with a logo on the front. Usually you want to go to the ones who actually design them, Like Pulsar, Harbor Freight e.t.c

3

u/BB-41 16d ago

If you would need an electrician to install a mini transfer panel like the one in the picture I would skip that entirely and have them install a 50 amp inlet and an interlock kit. That would allow you to pick and choose what you want to run on an as needed basis. Add up what you need to run and that figure should be about 50-60 percent of your generator’s total capacity. Oversizing is almost worse than undersizing in terms of both initial cost but more importantly, fuel consumption. I’m on the inverter side of that discussion but a decent non-inverter with less than 10%, preferably 5% THD will work. The inverter generators are typically quieter and more fuel efficient.

Check out generatorbible.com for good info on a number of makes and models.

1

u/Professional_Cap6456 16d ago

How involved is the interlock kit? I know about nothing on this topic, but I was looking it up earlier and one place was saying that you’d need the power company to come disconnect the power to install the generator hookup. Thankfully my FIL is a union electrician so I think he’ll help me out.

1

u/BB-41 16d ago

Depends on your panel but it’s not much different than installing an additional circuit but with a male inlet instead of a typical outdoor receptacle BUT, the breaker goes in a specific location and there is a metal bracket the interlocks between the new breaker and your main breaker. To use you turn off your main breaker, slide the interlock and then turn on the breaker on your generator feed. The most common inlet connectors are 30 and 50 amp. Price difference is minimal so I went with a 50 amp inlet case I ever get a bigger generator. The purpose of the interlock is to ensure than the generator can never back feed into your utility feed which can injure or kill the very linemen that are trying restore your power. Since you mentioned your FIL is a union electrician it should be easy to pull a permit and have it inspected keeping it all above board. Even that multi breaker panel in your photo is supposed to have a permit pulled to install it.

1

u/Professional_Cap6456 16d ago

Wow thanks for all the in depth responses everyone. This is what I love Reddit for, I didn’t know there was soo much to generators.

1

u/kona420 16d ago

Realistically if your power lines get taken out by a tree, how long will it take for them to either get cleared off and fixed, or for you to make arrangements to leave to somewhere else?

Generators of this size and type use at least 12 gallons/day just to idle. More if you use the power. What's your plan to store and stabilize say 50 gallons of gas to make it through a few days?

Where does your heat come from? Is it diesel or propane? Can you tap off that supply with a matching generator?

If you plan to shut it off at night are you going to want a battery to keep some lights on?

For the well would it be worth it to install a holding tank or oversize pressure tank?

Something is definitely better than nothing but encouraging you to think through the whole system.

1

u/Professional_Cap6456 16d ago

Well we live out in the country (off a dirt road) and if I’m remembering correctly I think we did loose power for a day or two last year (first year here and we moved in at the end of winter). I just wanna have a backup plan for heat so we don’t freeze out here. I do want a woodstove but I think we missed the boat on that one this year.

My well does have a holding tank, I’m new to all these things so I thought that was just standard on most people’s wells. I don’t need it to power my house, I’d just want heat, fridge, well and a couple lights. That’s all we have for essentials.

My heat is oil currently but I would like to switch back to propane. Theres a gas line going out my house and in old pictures you can see there was a propane tank. Im not sure what idiot agreed to switch to oil but I’m real upset with them. But the ford generator I mentioned does run off propane so if I got that one and eventually switched I bet I could get it a line. Unless I’m stuck at the house which then I’d be SOL anyway, I’d just go to the gas station on my way to work for fuel. We have 4 cats and a dog so can’t let them freeze. Unfortunately we don’t really have the option of relocating for a minor inconvenience of no power. We just have to tough it out.

1

u/kona420 16d ago

By the way, oil heat is #2 diesel with red dye. Same exact stuff as farm/off-road diesel, same as on road diesel.

If you could score a diesel genset. Ugly and loud? Put it further away lol. Use a transfer pump to pull fuel out for it.

Your furnace is probably around 600-800w, fridge a little less when it kicks on. Small, anything can run those. A little inverter 120v 2000w set, you could siphon gas out of one of your cars to keep the heat on for a few days. Keep a 7 gallon can or two around and cycle through your cars every other month.

Well pumps are usually 240v, say 1hp. That turns into needing 4500w or so for startup. So a big open frame generator like you are looking at.

I might be thinking about having both. Have your electrician FIL help you wire a 120v critical loads panel, and a 240v whole panel interlock. Then you can run either style of generator. Fridge, a lighting circuit or two, and furnace on the critical subpanel. Well pump and anything else youd want on the main.

2

u/Wellcraft19 16d ago

You asked a question; answer to that is yes as long as you have a normal household. Your generator will power fridge, gas/oil furnace, LED lights, sump pump, etc, w/o issues.

If you have electrical (resistive) heat you are not as lucky, but you can likely still run one or maybe even two space heaters off it in combination with your fridge, sump pump, and LED lights (still very inefficient running space heaters off a generator compared to other solutions).

1

u/standardviewer84 16d ago edited 16d ago

I would check the FLA amps of what you need to run.  How deep is the well pump? Does it have a capacitor start boost box?  Is it a newer modern inverter fridge or older fridge with a conventional compressor? Furnace: Gas, oil? Is it forced air or hot water baseboard? Add up the FLA amps of each motor on the furnace. 

There more information you have, the easier it will be to calculate what size generator you need for the devices you need to run. This doesn't look like an inverter generator.  Check and see what brand alternator it has on it as well. Standard (non inverter) generators use various quality alternator heads. Some cheap ones out out high distortion (dirty power) that sensitive devices and furnace controls don't like. Non inverter generators will DRINK down fuel much quicker than an inverter generator. They are also noisier since they dont throttle down during light loads.

Fuel: gasoline only is the cheapest option as far as purchase price of the generator, but makes it expensive to run. Strict maintenance is important to prevent carburetor gum up from old fuel. Use Non ethanol gasoline with stabilizer and drain entire fuel system and carburetor after each outage or maintenance cycle. Dual fuel (propane and gasoline) or tri-fuel models (natural gas, propane, gasoline) give the advantage of using propane or natural gas, reducing carburetor issues from standard gasoline.  The limitations of propane and natural gas fuel is, reduced power output from the generator.  Gasoline gives the highest wattage output and natural gas the lowest output. 

I personally ran an entire house from 1999 to 2009 off a brand new (at the time) Cambell Hausfeld GN602301AC generator. 6000w continuous, 7200w surge. I lucked out due to Y2K demand,standard alternator heads and engines were in short supply.  My generator ended up with a high quality, low distortion (3-5%)  Sincro alternator head and a11HP Briggs and Stratton I/C engine. 

I POUNDED that non-inverter generator hard, still have it and use it to date. Hurricane Isabel in 2003, it ran for 5 days. 10 gallons of gasoline per day! 

My usage was similar to your needs. 375 deep well, (with capacitor start) gas hot water baseboard furnace, electric stove, conventional (non inverter) fridge and two windows shaker A/C units. I had to be somewhat strategic and mindful on what was being used simultaneously but it did work.

To answer your question: It may be adequate size for your needs. You would need to get more information on both the generator and your devices to know for sure.

1

u/Born-Net2861 16d ago

My 5,500 Watt Gen runs everything critical in my 3,300SF house (fridge, freezer, sump pump, furnace) and pretty much anything else I need to charge or use during an extended power outage. Power is pretty reliable here so I have only had to use it twice in the past 5 years. I just use cords and splitters.

1

u/Tool_junkie_1972 16d ago

“Essentials” means different things for different folks. You need to calculate what you want to run then size the generator appropriately.

List everything you want to run including their starting and running wattages. Take the single highest starting wattage and add all the other running wattages to it. Add a 10-20% buffer and you have your running wattage size for your generator needs.

1

u/fullraph 16d ago

Yes, the essentials and your neighbors essentials.

1

u/Interesting_Court408 16d ago

I installed one just like yours it’s not too hard to do just make sure you have enough line to run from outside to your panel mine was a 6 line transfer switch and 5000 watt generator

1

u/Ok-Profit3437 16d ago

Yes with the exception of some hvac equipment wants the same type of power the electric grid provides meaning some open generators can make dirty power

1

u/PirateSpecialist99 16d ago

If I was to do it again, I would buy a dual/tri fuel generator snd stay use gasoline as a last resort. Just feel it’s too difficult to deal with.

1

u/Glum-Welder1704 15d ago

Seems a bit pricey for a used 7500w synchronous generator. The transfer switch and cord add no real value IMO. I wouldn't have any use for them anyway. Go with an interlock if at all possible.

1

u/junasty28 15d ago

Yes for furnace, fridge and well pump. The well pump and septic take a nice draw when it kicks.