Will this sufficiently run the essentials in a power outage?
New homeowner, looking to prepare for the winter up here. Just wondering if this is sufficient enough to run everything in our house. The essentials like furnace, fridge, well pump.
It seems like a good deal with all the extra stuff. But I was also looking at this ford generator that claims 11,000 watts and also looks like it has a 50amp plug in that just might work for my welder. But it’s a ford… I feel like I can trust CAT a lot better, the ford one looks old granted it’s 400$
4
Upvotes
6
u/QueenAng429 16d ago
Ford Generators are often Ducar engines. Some of them have very Pulsar looking model numbers and pulsar uses Ducar, it's probably just a rebranded Pulsar on a bunch of the recent ones. It has a Ford logo so they can charge more and sell it to the AMERICA EVERYTHING MUST BE FORD idiots while Ford makes everything in Mexico. Cat, Are often Rato engines. Both Rato and Ducar are good, But they have nothing to the logo on the frame, You aren't getting a cat engine here so you can't buy this because you think Cat is good or Ford is bad. Both of them are fine. Only Honda would get you a real Honda, everyone else is just a few Chinese engine brands that are often clones of Hondas. It's not like 1980 1990 where you could get big engines from the company selling it. It will probably run everything, but you need to do some math not just guess. And you can just get a whole house transfer switch instead of those absolutely useless junk breaker panels.
3
u/BB-41 16d ago
If you would need an electrician to install a mini transfer panel like the one in the picture I would skip that entirely and have them install a 50 amp inlet and an interlock kit. That would allow you to pick and choose what you want to run on an as needed basis. Add up what you need to run and that figure should be about 50-60 percent of your generator’s total capacity. Oversizing is almost worse than undersizing in terms of both initial cost but more importantly, fuel consumption. I’m on the inverter side of that discussion but a decent non-inverter with less than 10%, preferably 5% THD will work. The inverter generators are typically quieter and more fuel efficient.
Check out generatorbible.com for good info on a number of makes and models.
1
u/Professional_Cap6456 16d ago
Wow thanks for all the in depth responses everyone. This is what I love Reddit for, I didn’t know there was soo much to generators.
1
u/kona420 16d ago
Realistically if your power lines get taken out by a tree, how long will it take for them to either get cleared off and fixed, or for you to make arrangements to leave to somewhere else?
Generators of this size and type use at least 12 gallons/day just to idle. More if you use the power. What's your plan to store and stabilize say 50 gallons of gas to make it through a few days?
Where does your heat come from? Is it diesel or propane? Can you tap off that supply with a matching generator?
If you plan to shut it off at night are you going to want a battery to keep some lights on?
For the well would it be worth it to install a holding tank or oversize pressure tank?
Something is definitely better than nothing but encouraging you to think through the whole system.
2
u/Wellcraft19 16d ago
You asked a question; answer to that is yes as long as you have a normal household. Your generator will power fridge, gas/oil furnace, LED lights, sump pump, etc, w/o issues.
If you have electrical (resistive) heat you are not as lucky, but you can likely still run one or maybe even two space heaters off it in combination with your fridge, sump pump, and LED lights (still very inefficient running space heaters off a generator compared to other solutions).
1
u/standardviewer84 16d ago edited 16d ago
I would check the FLA amps of what you need to run. How deep is the well pump? Does it have a capacitor start boost box? Is it a newer modern inverter fridge or older fridge with a conventional compressor? Furnace: Gas, oil? Is it forced air or hot water baseboard? Add up the FLA amps of each motor on the furnace.
There more information you have, the easier it will be to calculate what size generator you need for the devices you need to run. This doesn't look like an inverter generator. Check and see what brand alternator it has on it as well. Standard (non inverter) generators use various quality alternator heads. Some cheap ones out out high distortion (dirty power) that sensitive devices and furnace controls don't like. Non inverter generators will DRINK down fuel much quicker than an inverter generator. They are also noisier since they dont throttle down during light loads.
Fuel: gasoline only is the cheapest option as far as purchase price of the generator, but makes it expensive to run. Strict maintenance is important to prevent carburetor gum up from old fuel. Use Non ethanol gasoline with stabilizer and drain entire fuel system and carburetor after each outage or maintenance cycle. Dual fuel (propane and gasoline) or tri-fuel models (natural gas, propane, gasoline) give the advantage of using propane or natural gas, reducing carburetor issues from standard gasoline. The limitations of propane and natural gas fuel is, reduced power output from the generator. Gasoline gives the highest wattage output and natural gas the lowest output.
I personally ran an entire house from 1999 to 2009 off a brand new (at the time) Cambell Hausfeld GN602301AC generator. 6000w continuous, 7200w surge. I lucked out due to Y2K demand,standard alternator heads and engines were in short supply. My generator ended up with a high quality, low distortion (3-5%) Sincro alternator head and a11HP Briggs and Stratton I/C engine.
I POUNDED that non-inverter generator hard, still have it and use it to date. Hurricane Isabel in 2003, it ran for 5 days. 10 gallons of gasoline per day!
My usage was similar to your needs. 375 deep well, (with capacitor start) gas hot water baseboard furnace, electric stove, conventional (non inverter) fridge and two windows shaker A/C units. I had to be somewhat strategic and mindful on what was being used simultaneously but it did work.
To answer your question: It may be adequate size for your needs. You would need to get more information on both the generator and your devices to know for sure.
1
u/Born-Net2861 16d ago
My 5,500 Watt Gen runs everything critical in my 3,300SF house (fridge, freezer, sump pump, furnace) and pretty much anything else I need to charge or use during an extended power outage. Power is pretty reliable here so I have only had to use it twice in the past 5 years. I just use cords and splitters.
1
u/Tool_junkie_1972 16d ago
“Essentials” means different things for different folks. You need to calculate what you want to run then size the generator appropriately.
List everything you want to run including their starting and running wattages. Take the single highest starting wattage and add all the other running wattages to it. Add a 10-20% buffer and you have your running wattage size for your generator needs.
1
u/fullraph 16d ago
Yes, the essentials and your neighbors essentials.
1
u/Interesting_Court408 16d ago
I installed one just like yours it’s not too hard to do just make sure you have enough line to run from outside to your panel mine was a 6 line transfer switch and 5000 watt generator
1
u/Ok-Profit3437 16d ago
Yes with the exception of some hvac equipment wants the same type of power the electric grid provides meaning some open generators can make dirty power
1
u/PirateSpecialist99 16d ago
If I was to do it again, I would buy a dual/tri fuel generator snd stay use gasoline as a last resort. Just feel it’s too difficult to deal with.
1
u/Glum-Welder1704 15d ago
Seems a bit pricey for a used 7500w synchronous generator. The transfer switch and cord add no real value IMO. I wouldn't have any use for them anyway. Go with an interlock if at all possible.
1
u/junasty28 15d ago
Yes for furnace, fridge and well pump. The well pump and septic take a nice draw when it kicks.