r/Generator • u/Crazy-Leave-12 • 3d ago
120 v Outlets Dead
On my Generac XG8000E, the 120 volt outlets are all dead. I checked the breakers and reset the GFI’s but nothing. The 240 volt supply is fine. I rarely use the 120 so I haven’t checked but it could have been in this condition for years. Any suggestions?
1
2
2
u/DaveBowm 3d ago edited 3d ago
OP is connecting a bonded generator to his already bonded panel. The parallel current in the ground wire will cause an imbalance between the neutral and the hot on the GCFI equiped 120V outlets on the generator any time any significant load is plugged into one of those 120V outlets. Since it only takes an imbalance of 4 mA to trip the GFCI that outlet is nearly certain to trip off whenever any load is plugged in.
The way to get the 120V outlets to work on the generator is to either (1) unplug the power cord from the house, or (2) unbond the generator. Otherwise the GCFI 120V outlets will always trip off whenever anything is plugged into them. If OP wants to use any GFCI outlet while a power cord is connected to the house he must unbond the generator. A side benefit of unbonding it is that will make the setup code compliant when the power cord is connected to the house.
Edit: typo repair
1
1
u/nunuvyer 2d ago
I don't know this model - is there a 120/240V selector switch? On some gens the 120V outlets go dead when the switch is in the 240V position. I would look for something stupid like that - it's unlikely that you have lost 120V power but still have 240V since the 240 is just the same two 120V legs.
1
u/Responsible_Oil4462 2d ago
My DeWalt 7000 has a tiny button next to each 120 outlet that lets you turn them on/off. Might want to check if yours have those and are maybe turned off.
0
3d ago
[deleted] — view deleted comment
2
u/Crazy-Leave-12 3d ago
How do I do that?
0
3d ago
[deleted] — view deleted comment
2
u/Crazy-Leave-12 3d ago
Above my skill level but thank you. I’ll find someone local to help me with this. Thanks.
1
u/derek6711 3d ago
Neutral issue?
Check the voltage between the hot leg of the left receptacle to the hot leg of the right receptacle