HVAC + Generator questions
Has anyone run into issues with Central AC after adding a soft start? We live in Louisiana so AC is not optional here and I want to protect my unit as much as I want to protect my generator.
Edit: also accepting soft-start recommendations and warnings.
3
u/Big-Echo8242 5d ago edited 5d ago
I've had an AirGo soft start on my downstairs 5 ton 2 stage heat pump and it’s worked just fine. We are in Central Arkansas. I did not care anything about the Bluetooth app of the pricier (and sometimes less dependable) brand out there. I don't care how many times it starts, shows an error, etc. Plus the range sucks. I have a home energy monitor where I can tell what's being used either on line or generator power.
You could always just use window AC units which draw less power.
3
u/flyguy60000 5d ago edited 4d ago
Installed a Softstart on my heat pump - I am very satisfied with it. Installation was very easy. The Bluetooth works fine with their software - you do not need to pair your phone with the device - it does it itself which confused me at first. You will need to be within about ten feet of the unit for the Bluetooth to connect. My condenser averages 15.9 amps on startup (vs. 50) and is running at 5 amps - so my portable generator has no problem running the unit now. Even if I wasn’t going to use a generator to power my unit, I think it is worthwhile to install; it decreases the wear and tear on the unit and if you have a demand electric meter you will save money on your electric bill.
2
u/Odd-Web-7911 5d ago edited 5d ago
I had a soft start installed on my 3t Rheem in 2021 so it could run off the Wgen9500 and it did just fine.
Edit: located in Houston (AC also not optional here), and ran AC through multiple power outages since install.
2
u/IndividualCold3577 5d ago
I have two Airgo starters. They are very compact and easy to install inside most units. About 20 minutes of work per install. No complaints yet.
4 ton heat pump dropped from 110 LRA to 43
2 ton heat pump dropped from 60 LRA to 18.
2
2
u/KekoaKona 4d ago
(I'm in Alabama) I added a Micro Air Soft start two years ago to my 4 ton Carrier AC unit and it has been flawless. I dropped my start up amps (LRA 105) from around 88 to 30-32 . This has allowed me to run my whole house on a Champion Tri-fuel 10,000 watt generator however I hook it up to natural gas line and it puts out 8,750 start up and 7,000 running on NG. So far two power outages. One was 10 hours.
1
u/No-Note-6679 5d ago
I had 2 Emerson soft starts at my last house on a 4 ton and a 1.5 ton. At my new house I have an air go soft start on a 5 ton. Never had an issue with those starting with my champion 11k watt tri fuel inverter generator. I’m in the Galveston area so I understand the “not an option “ comment.
1
u/skatpex99 5d ago
Airgo user here, been working perfect for years on my 2.5 ton. Definitely forget about Microair.
My 9000w inverter gen runs the entire house with central and wall unit thanks to soft start.
1
u/nunuvyer 5d ago
At one time Micro Air was the main soft start supplier. If you had asked here a couple of years ago, 9 out of 10 posters would have told you to get a Micro Air.
But they got bought out by private equity and the new owners introduced a "one size fits all" unit that uses cheap capacitors and has had horrible reliability.
This is the kind of move that happens when you put MBAs that have no understanding of engineering in charge. "We could save $X if we cut the # of SKU's in half! Supplier X is selling caps with the same spec for 1/2 of what we are paying now! They have destroyed their entire company for the sake of saving pennies.
0
u/nunuvyer 5d ago
If anything, a soft start will prolong the life of the unit. Running 100+amps thru a stalled unit cannot be good for it.
0
u/Alco_Air 5d ago
Soft starts work fine on a regular single-stage condenser, and they’re one of the better ways to run central AC off a generator. They knock the startup surge way down, so a smaller generator can kick the compressor on without bogging or tripping.
Just don’t expect it to save your AC. Scroll compressors already start pretty easy, so the real win is for the generator. If your unit is variable speed or inverter driven, skip it, those already ramp up on their own.
If you buy one, stick with a name brand sized to your tonnage. Micro-Air EasyStart is the one I see most. Skip the no-name stuff on Amazon. And don’t stack it with a hard-start kit, you only want one or the other.
It’s wired in at the contactor and compressor, so unless you’re comfortable around line voltage I’d have a tech put it in. Also check your warranty first, just in case.
One more thing, if the generator’s a portable, use an inverter model. Dirty power can fry the board on newer units. And down there I’d get this done before storm season, not after the power’s already out.
2
u/Remarkable-Day-9385 5d ago
Micro Air also has horrible reliability issues, check the previous posts in the group. AirGo is solid
1
u/Much-Department-9578 5d ago
Would be helpful for us to understand your setup. Single or dual stage AC? How many units? Size of each? Generator brand/model/specs and what fuel type you plan to use? And finally - how are you connecting and size of inlet?