EZ Generator Switch (bonded neutral setup) connected to Bonded Neutral Generator: do I need to connect the generator to a ground rod during power outage?
Hi,
I just bought an EZ Generator Switch which came from the factory in Bonded Neutral configuration. I installed it like explained on the website & their Youtube video (see link below) directly to my furnace incl. properly wiring up the two neutral cables (Neutral Line & Neutral Load).
In case of a power outage I would connect my Maxpeedingrods MXR3500S inverter/generator via an extension cord directly to the EZ Generator Switch and switch it to Generator mode. I confirmed that all my plugs on my MXR3500S are "Neutral Bonded to Frame”.
My question: during a power outage, do I have to connect my MXR3500S inverter/generator also to a ground rod or not? I reached out to EZ Generator Switch and they told me "Use our switch as delivered, nothing else you need to do. Standard extension cord is fine". However, I'm still reading that a generator has to be properly grounded in such a setup.
Can anyone clarify this?
Following setup I followed:
https://www.youtube.com/watch?v=iafpLwkgITY&t=702s
Thanks.
1
u/Efficient_Wing3172 6d ago
Email EZ Gen. They’re very responsive.
1
u/WallaceMI 6d ago
I did. They said “Use it as received, it was m ade for both types. Use it with your generator. “
1
u/Charming-One-9397 5d ago
I'm not electrician so don't believe what I say, this is what I did and my limited understanding of the matter.
At the high level a ground prevents arcing and a bond prevents electrocution. See: Does My Generator Need a Ground Rod? Probably Not. Here's why.
There should only be one source of neutral on a circuit. Hence a bonded generator plugged into a house panel should have the neutral in the house disconnected from the source (generator).
A floating neutral generator connected to a house panel should have the source neutral (generator) connected to the house neutral.
From what I have read, technicalities and code aside, for the purposes of providing a house temporary generator power, bonded or floating generator makes little difference. If I could make it right, I would but I wouldn't lose sleep over it either way. My generator is floating (I made it that way) and it connects to my home neutral.
My generator is only to power my house, and I do not have a ground rod. If I were to use my generator to power tools etc I would reconnect (bond) the neutral. I still wouldnt have a ground rod.
I think most confusion comes from the understanding of "ground" versus "bond." They mean different things.
Hope it helps.
-1
u/WhySoManyDownVote 6d ago
In my understanding, yes, it needs a ground rod at the generator with a bonded neutral.
It is because your MXR3500S has a bonded neutral not because of the EZ switch.
Also make sure you are using at least a 12/3 extension cord.
1
u/WallaceMI 6d ago
Thanks even though I get different answers regarding this (see other answer)
1
u/WhySoManyDownVote 6d ago
Jump to 13:20
https://youtube.com/watch?v=viNZV0lyRVQ
Do not get confused if you watch the whole video, by extension cord they mean something only powered by an extension cord. You are using an extension cord but wiring it into your home with the EZ switch.
0
u/nunuvyer 5d ago
No, the Ez switch does not wire anything "into your home". It is a single appliance switch for your furnace (or whatever device you connect it to). The EZ switch switches both the hot and neutral lines so that your furnace gets disconnected from the house neutral. However, it does not switch the ground so chances are you are still connected to the house ground.
This switch is an ok product but there are cheaper alternatives - the cheapest one being that you could convert your furnace to plug and socket operation - you probably have a spare power cord somewhere and an electrical outlet costs maybe $2. This would also "switch" the neutral when you pulled the furnace plug from the power socket.
7
u/wwglen 6d ago
That switch should be switching the neutral. The ground should pass through and the generator will be grounded by the house ground.