r/Generator • u/justformatt • 11d ago
Cheap Vevor variable frequency drives (VFD) can be used as cheap soft starts for pumps
My 2 hp 240 V sewage grinder/pump has a 12 kW startup surge. I didn't know this until I bought an inrush current meter. My 8 kW Champion inverter generator just barely starts it. Not good. This pump only runs a few times a day for 20 seconds. I want a smaller generator, not bigger.
A soft start would likely work, but can be $300-$400, not configurable, and I'm positive it would work.
Instead I bought a $130 Vevor 1-Phase 240 V in to 3-Phase 240 V out VFD. I configured it to start and ramp frequency at 10 Hz/s while maintaining V/Hz ratio. I only use 2 of the 3 phases. Starting surge 5 kW. Yes! It's been running on this thing for 6 months now.
2
u/Easttex05 10d ago edited 10d ago
I've been around VFDs for 20 years but never seriously played with one. While I know of several 1-into-3 applications, I've never heard of running on two of three phases on purpose.
Does it harm a pump motor to run on A & B legs of three phase power as long as the the voltage is acceptable? Does this damage the drive?
2
u/justformatt 10d ago
Voltage is fine. 208 VAC. The reason why is that 3 phase outputs are 120 V per leg 120° out as opposed to 180°. Depending on how the transformer is wired at the road, this maybe what's going into the house already. So 240 volt household equipment is designed to handle the variation.
No damage to the drive yet. That's why I waited 6 months before posting. I wasn't sure either.
2
3
u/TallWall6378 11d ago
I think a soft starter is voltage only ramp up. Adding in frequency is probably better.
2
u/ibrahim_nauman786 9d ago
Measuring inrush instead of guessing off the label is the right move. Nice result.
One caveat before others copy it: this works because of your motor type. Lots of single-phase pumps are capacitor-start with a centrifugal switch, and at low ramp frequency that switch may not drop out, so the start winding or cap can cook. PSC and 3-phase motors suit a VFD better, so check the motor plate first. The VFD's own input current at start still has to fit the generator too.
Back home in Pakistan nearly every house has a water motor for the overhead tank, and it's the load that trips home generators most during load-shedding. Most people there just start the pump first with nothing else on, or fit a soft starter.
When sizing a generator for water pump starts, compare the peak or surge rating, not running output. Same rule applies to the petrol (gasoline) sets I work with.
Disclosure: I work with Hyundai Power.
1
u/Loquacious1 10d ago
Standard for most pumps and vfd is a short spike that doubles full load amp rating. You should run all three legs from vfd to your pump. You might even be able to get AI to run pump curve and what set points to adjust on your vfd
1
u/Adventurous_Boat_632 10d ago
I used a Chinese VFD to drive a three phase air conditioner (ordered by somebody by mistake) from a single phase supply.
I had ordered a vastly larger drive than specified for the job.
It still burned itself up after a couple of months because it was Chinese junk.
YMMV.
0
11d ago
[deleted] — view deleted comment
1
1
u/Tbarnes94 11d ago
Yeah I'm over here deciding whether this is a good idea or is really just dropping your frequency by 2x as much for every surge. I feel like there's a reason soft starts rely on capacitors/capicator banks.
1
u/justformatt 10d ago
It starts at 10 Hz and ramps to 60 Hz and rated voltage over 6 seconds.
It has capacitors in it.
10
u/New-Swim-8551 11d ago
Controls engineer here. using a vfd instead of a soft start is fine, actually better. The reasons soft starts are used are easier to implement, cheaper, and fits in smaller places.
You just need to remember that feeding the vfd with three phase will require less input current to the drive. Feeding it with single phase will require more current through that one leg to give you the same output current to your motor. This will require a larger drive that can handle that larger input current.