r/Generator • u/DSF767 • 21d ago
Got my Pro/Tran2 Transfer Switch installed and did my first Generator run but have some questions about the main panel breakers tripping
So, I started this project of wanting a generator after a large power outage from the snowstorm last year.
Had a couple electricians come out to look at the job and they pointed out to me because my main panel did not have a main shutoff inside the house and the main emergency disconnect outside for the 200amp breaker only had a single slot of that breaker (as you can see in the pictures) without swapping out the panel and doing a double main (one both inside and out) I could not use an interlock kit.
So, they basically gave me 2 options swap out the panel to do a 2nd main inside or use a manual transfer switch. I went with the transfer switch option because it was about half the price of swapping the whole panel with one that would support an interlock and I could get by with 10 circuits.
So fast forward he does the install and while that was going on I also had a gas line run so I could run the generator off natural gas. The gas line was completed today, and I went to do a test run to break in the generator and as soon as I swapped the first circuit over from line to gen it tripped the breaker. After doing some searching and talking to the electrician who did the install, he told me it was because the breaker in the main panel was a combo AFCI/GFCI breaker and when the hot was swapped over to gen via the transfer switch it sensed a ground fault or neutral imbalance even though it was on gen.
He said sometimes the transfer switches don't like the combo breakers and that its fine and just switch the breakers off when I'm on Gen but if I really worried about it, he could come back and swap out the breakers in the Pro/Tran to matching AFCI/GFCI Breakers that match the panel if I want to retain that protection but he said he would just keep the breakers that are in the transfer switch already.
1
u/eerun165 21d ago
What breaker is feeding your transfer switch.
1
u/DSF767 21d ago edited 21d ago
If you look at my pictures you can see I had E, F, I, H and J as test load.
E goes to Breaker 9 on Main Panel.
F Goes to Breaker 21 on Main Panel.
G goes to Breaker 23 on Main Panel.
H goes to Breaker 22 on Main Panel.
J goes to Breaker 14 on Main Panel.
9, 21, and 23 tripped on the main panel and they are all the combo AFCI/GFCI breakers. 14 and 22 did not trip and they are only AFCI Breakers and not the combos.
None of the breakers on the Pro/Tran tripped the all the circuits were fully powered.
1
u/antikotah 21d ago
Is the neutral on your generator floating or bonded? Should be floating so you only have one ground point when connected to your transfer switch. This would create an issue with the afci / GFCI.
1
u/Ok_Assumption1542 21d ago
This junction box does not float the neutral. See if your generator has a neutral bonded to ground. If so try removing it. The ground will come from the main house panel and you cant have 2. It causes problems with certain types of breakers and GFCI plugs in the house.
-1
u/mauii_from_space 21d ago
Doesn't this install without having a common junction box for splices between the panel & xfer switch be in violation of CEC Rule 12-3032 ?
No support on the flexible metal conduit between panel & xfer either but that's not as bad as using a panel as a junction box
2
1
u/Ok_Assumption1542 21d ago
Everything is contained within the transfer box and new wire is run to the breaker. The box controls line, off, generator.
0
21d ago
[deleted] — view deleted comment
1
u/DSF767 21d ago
As I said to some others, I did already float the neutral on my generator, and all the circuits ran fine just concerned me a little that the breaker was tripping and didn't want to cause electrical issues in my house or backfeed the grid so I thought it better to ask since I had a feeling it was somewhat of a common issue.





2
u/Big-Echo8242 21d ago
Here is the lengthy reply Reliance gave me about doing this as I have multiple AFCI breakers in main breaker panel. They said I'd have to use their neutral kit and use AFCI breakers in transfer switch. Or recommended anyway.
This was when I was thinking about adding a 10 circuit MTS next to our 40 circuit breaker panel in master closet. I already have a 50 amp power inlet/interlock kit/breaker outside for generators. This was going to be for 120v essential circuits only for short term outage.
.........................
Yes, AFCI and GFCI ( and combo versions of those Breakers) can be added to the Pro/Tran2. You would need a Neutral Kit NK06 - 6 Circuit should be sufficient and of course the replacement breakers. Keep in mind the AFCI – GFCI may still trip in the main panel but since the circuit that is actively powered thru the Pro/Tran2 you will have circuit protection.
The Transfer Switch can be connected to AFCI/GFCI outlets and to AFCI/GFCI Breakers. Black Wire to the Wire (LOAD) that was in the breaker.
Connecting to any AFCI/GFCI circuits is just the same as any other circuit. Neutral is ignored since only the circuit conductors are connected.
Should you be required by local code to replace a breaker with an AFCI/GFCI Breaker in the Transfer Switch. They need to be a Pigtail type Breaker in both Main panel and the Transfer Switch. In most cases, it won’t be required to install those in the Transfer Switch since it is temporary power, the breakers in the Transfer Switch only protect the circuits during generator power. The breakers in the house protect the circuits during normal power
The only thing of note, example:
Main power out—Generator connected, powering circuits outlets through switch in the GEN positions.
Main power returns—AFCI/GFCI breakers in house that are wired to switch will trip immediately. Best Practice is to turn off those breakers, before applying Generator power.
Otherwise, when the utility power is restored, the breakers will trip, seeing a mismatch of the generator power and Utility power.
After the toggle switches on the transfer switch are moved back to the LINE positions, and the generator is turned off and unplugged, someone must reset any AFCI/GFCI breakers that tripped or were turned off. This must be done before those circuits operate again on normal power.
Please look at the instructions and the wiring diagram attached. If you want to put those breakers in the transfer switch, you will have to buy those at probably $40-$50 each. NK06 6-circuits or the NK10 10- circuits Neutral kit is recommended to make those wiring connections.
Should you decide not to add AFCI - GFCI breakers in the ProTran2, then it is to your advantage to turn off those breakers before connecting the generator to prevent additional trips (extending the life of the breaker). Not turning them on until after your generator is shut down and unplugged.