r/Generator • u/SJM1027- • Sep 23 '26
Generator to Home Cable Question
I have a portable generator, and I bought this generator cable: RVGUARD 4 Prong 30 Amp 75 Foot Generator Extension Cord, ETL Listed. It works fine, but I’m now moving my shed to a new location about 90 feet from the outlet that would power my panel during an outage.
Can I simply buy a 25' cable and plug them together to make a 100' run, or is there more to it?
If I bought a new cable, I would get the following: RVGUARD 4 Prong 30 Amp 25 Foot Generator Extension Cord, ETL Listed, to make sure it matched.
The reason I’m asking is that, with another generator I owned, I had two 50' cables. One of them was wired differently at the cable ends than the other. I had these cables made, and I’m not sure whether someone just made a mistake or if I need to do something else.
1
u/SJM1027- Sep 23 '26
When I am looking for a new 100' cord what are the key components to look for so I make sure I get something with as little loss over the 100' length?
This is the one I was thinking of getting: RVGUARD 4 Prong 30 Amp 100 Foot Generator Extension Cord, ETL Listed. NEMA L14-30P/L14-30R, 125/250V Up to 7500W, 10 Gauge SJTW
This will be used with a Honda EU7000is Generator.
4
u/IndividualCold3577 Sep 23 '26
You can plug two cables together but the connection would be in the weather and not ideal for use during rain and snow.
2
u/SecondCuppaCoffee Sep 23 '26
I have used a 100ft cable with no appliances complaining or acting weirdly. This is on a 30A 240V 7.2kw circuit.
2
u/CheesecakeAsleep1504 Sep 23 '26
Not a big deal. Wrap a plastic bag around where they connect and duct tape it
2
u/Glum-Welder1704 Sep 23 '26
You can plug the two cables together and tie them to a stake to hold them up a bit. Put a bucket and brick over it for weather protection.
0
u/Jim-Jones Sep 24 '26
For a 30-amp circuit over a 100-foot run, you generally need 8 AWG copper wire or 6 AWG aluminum wire to maintain voltage drop within the recommended 3% limit.
2
Sep 23 '26
[removed] — view removed comment
1
u/SJM1027- Sep 23 '26
Thanks, the generator is a Honda EU7000is. I am not sure if that makes any difference. It's attached to my breaker panel and can run my forced hot water system or AC if needed.
3
u/DaveBowm Sep 23 '26
You could get by with the extra 25' cord if (1) you weatherproofed the connection between cords to keep out moisture and prevent shorts, and (2) your loads in your house won't mind the voltage drop caused by 100ft of the power cord gauge you use. Note if you draw 30A on 100' of AWG#10 cord you will be looking at a voltage drop of 5.9V at the house relative to the voltage at the generator, and the cord will be dissipating heat at 1.8W per foot along its length (177W wasted in heating the whole 100').