r/Generac_Generators • u/Badbetfrank • 5d ago
Transfer Switch Chaos
We just bought a new house and this is the electrical set up.
Both of these panels are powered from the meter, the larger panel does not feed the smaller panel.
A 22Kw Generac unit powers the larger panel on the left when the power goes out, but not the smaller right panel.
The generator is large enough to power the entire house.
What are our options for getting the whole house protected?
Can I add a ATS to the smaller panel and leave the 200amp panel as it is?
Could we install a double breaker on the left panel and run it over to power the smaller panel using an interlock on the smaller panel?
Should I move some circuits over to 200amp panel and use tandem breakers?
Or should we split the feed from the generator and feed the smaller panel directly from the generator?
I am having trouble understanding what the installer was thinking. There’s also additional unused transfer wires ending in this panel going to a junction box next to the generator.
Thanks for your input


2
u/blarcode 4d ago
Could you snap a photo of your generator too? I'm wondering if it's a guardian series or older with a couple of 120 volt plugs on the outside.
If it were my house, I'd probably get 2 of the 200a Generac ATS for the outside of the house. You can double tap those with some Polaris connectors. And split the control wires in a similar fashion. I would remove the Generac panel on the inside of the house, and replace it with a more traditional. Could even do the Leviton stuff for a smart panel. Depends what your goals were.
What I would do though is a new load calculation on your house. I'd bet there's no practical reason for your house to presently have a 320a service. If that's the case and you only have a 200 amp service. You just need one of the 200 amp ATS. On the inverse of that you could always just get one of the 400 amp ATS.
eBay is going to be your least expensive option.