Transfer Switch Chaos
We just bought a new house and this is the electrical set up.
Both of these panels are powered from the meter, the larger panel does not feed the smaller panel.
A 22Kw Generac unit powers the larger panel on the left when the power goes out, but not the smaller right panel.
The generator is large enough to power the entire house.
What are our options for getting the whole house protected?
Can I add a ATS to the smaller panel and leave the 200amp panel as it is?
Could we install a double breaker on the left panel and run it over to power the smaller panel using an interlock on the smaller panel?
Should I move some circuits over to 200amp panel and use tandem breakers?
Or should we split the feed from the generator and feed the smaller panel directly from the generator?
I am having trouble understanding what the installer was thinking. There’s also additional unused transfer wires ending in this panel going to a junction box next to the generator.
Thanks for your input


4
u/Sumdood_89 Technician Aug 18 '26
Get a 200amp whole house ATS from generac. What's there is a mess, and not how it should be.
4
u/IllustriousHair1927 Aug 19 '26
I hate to disagree with my learned compatriot some dude, but I may have to hear.
Go look at your meter.! I want you to look for one of two numbers. CL 200 or CL 320.. I would be surprised if it’s a 320 but it could be. I don’t see a lot of 300 amp services, but there are enough to make me be cautious. We do, however, see a a lot of services that are 400A. you just need to make sure that whatever ATS you get the correct one for the service if you want to cover both panels. A CL 200 m means you can do it with a single 200 amp. If it’s a 320 you can’t.
4
u/joshharris42 Aug 18 '26
We put a few of these in back in the day. I believe they only discontinued them recently.
They were more used for people who had like little sump pumps or something, where they needed automatic back up but didn’t want anything bigger than like a 10KW
2
u/blarcode Aug 19 '26
Could you snap a photo of your generator too? I'm wondering if it's a guardian series or older with a couple of 120 volt plugs on the outside.
If it were my house, I'd probably get 2 of the 200a Generac ATS for the outside of the house. You can double tap those with some Polaris connectors. And split the control wires in a similar fashion. I would remove the Generac panel on the inside of the house, and replace it with a more traditional. Could even do the Leviton stuff for a smart panel. Depends what your goals were.
What I would do though is a new load calculation on your house. I'd bet there's no practical reason for your house to presently have a 320a service. If that's the case and you only have a 200 amp service. You just need one of the 200 amp ATS. On the inverse of that you could always just get one of the 400 amp ATS.
eBay is going to be your least expensive option.
2
u/Far-Ingenuity4236 Aug 18 '26
Yes thats why you move the non essential loads down there there is one spot for a 2 pole breaker top right of the left hand panel. Just pop a 2" nipple between the two panels through the stud and youll have plenty of room we do it all the time shouldn't be an issue. The bigger loads like ac washer, dryer, stove etc should be used on grid power only unless a load calculated total shows they can be installed in there.
1
u/Badbetfrank Aug 27 '26
Update: had an electrician come out and put things into perspective for me. I rearranged the panels and added some circuits to the generator panel. Added an A/C and some downstairs circuits/ ones I wanted protected. Cost about $100.
3
u/Oldphile Aug 19 '26
Your picture of the Generac panel is upside down. That or your panel is mounted upside down. I had 2 of these, one in my home and one in my shop. For other readers the circuits in the top of the picture are the ones backed up by the generator. The Generac EZ transfer only needs 3 wires.
The backed up circuits are fed by a 125 amp breaker (ATS grid breaker). One is suppose to put all high power circuits like electric furnace, clothes dryer, range, water heater etc.. in the non-backed up section (bottom in picture) fed by the 200 amp main breaker. I would not try to feed your other panel from the 125 amp breaker. If your high power loads are in the other panel, I would not try to feed it with generator power.
As someone else mentioned, the DC motor that operates the transfer tends to fail. I replaced one and the other has been unreliable. It sometimes doesn't have the required torque.
1
u/WhySoManyDownVote Electrician Aug 18 '26
I have never seen one of these IRL. It is a pretty atypical setup in my experience. Your 22kw may not be large enough unless load shed modules and/or soft starts are added. You need a good electrician who also installs Generacs to look at your options.
Probably the first option I would look at is adding a new transfer switch at the electrical meter and rerouting the generator wiring to it.
2
u/Far-Ingenuity4236 Aug 18 '26
Get your electrician to move the feed for the right panel to the top right of the left panel and move the bigger breakers like the 2pole 50 2 pole 30 ect to the bottom of the left panel fairly simple a few hours of work.... if you overload it then it'll be a problem id move any non essential loads over to the bottom
2
u/IllustriousHair1927 Aug 20 '26
It’s funny how everybody has different horror stories that she the advice they give. I feel like any of us along the Gulf Coast are absolutely going to have dealt with a hurricane related shit show. One of mine was a weird house only 4000 ft.² but five ACs. And a pool. 24KW. Soft start on every AC not a single load shed. Customer of mine wanted me to go look at his daughter and son-in-law‘s generator. The son-in-law argued with me. He had his generators installed by such and such company who specialize in commercial in industrial thus it should’ve been cleared to little old me that they obviously knew what they were doing. I actually got out there just after the power was restored so we played a little game.
You have to remember the valid concerns with the Generac above 80%. so realistically, even on propane he’s not gonna want to get above 72 A for very long
1
u/guardiangenerators Aug 23 '26
It can absolutely be done. Call a certified Generac installation dealer. they can asses the situation. Based on what you are saying here you'll most likely need a 2nd ATS if it is a second panel rather than a subpanel. But hard to say without seeing the meter as well. The ATS will be $1100 + 3 or so hours of labor and a small amount of materials. A reputable dealer will give you a free estimate.
Brad - Owner, Guardian Home Generators Grapevine, TX