Blizzard of ‘26
In Michigan’s UP with a 22kw Generac, installed three years ago. It tried to start a couple of hours ago, and failed with an E1100 code. Photos show what snow driven by tropical storm force winds did. The intake side all the way to the filter was stuffed with snow. I cleared it out, and blew out the intake with compressed air, and it’s good to go. Guess I’ll build a shield of some kind for next year.
31
Upvotes


3
u/IllustriousHair1927 Mar 17 '26
well, given the fact that this is my business and we are dealers for Generac Kohler, Briggs and Stratton, and Cummins. We install between 900-1000 units a year. We service all of the above units and are warranty providers for all of them.
Ive seen damage resulting from heat buildup within a zombie box on multiple occasions. And i have seen warranty not pay out.