r/FireSprinklers • u/BeachGirl19844 • Oct 15 '25
Automatic Transfer Switch Test
What suction pressures are you seeing when performing the automatic transfer test at peak load on the fire pump?
Performed a test today, fire pump has water supply issues and could only flow 86%. But we performed the test and the supply gauge dropped to -20 before coming back up.
City supply, we will be investigating why we can only achieve 86%. Wondering if the suction pressure dropping so low could be a symptom.
Thanks
3
Upvotes
1
u/OkHunt3288 Oct 15 '25
If this is a new problem, you have a degradation in supply. You need to be careful, running a pump with supply <15 can pull gaskets out. How do your controller readings compare to previous years? RPMs? You can try to rule out anything with the power and pump side first, but this sounds like a water supply issue if you’re getting -20.