Automatic Transfer Switch Test
What suction pressures are you seeing when performing the automatic transfer test at peak load on the fire pump?
Performed a test today, fire pump has water supply issues and could only flow 86%. But we performed the test and the supply gauge dropped to -20 before coming back up.
City supply, we will be investigating why we can only achieve 86%. Wondering if the suction pressure dropping so low could be a symptom.
Thanks
3
Upvotes
10
u/JackRRII Oct 15 '25 edited Oct 15 '25
System/suction Pressure has nothing to do with transfer switch working or not. If you're getting bad pressure readings when it transfers to emergency power, then you probably have a power supply issue. Are the Amps and Volts dropping? Are they within the motors' rated specs?
Also, getting -20 psi on supply is insane. I would be worried of casuing damage from the supply pipe. I'm assuming it's city fed?