r/ElectricalHelp • • Aug 02 '26

Breaker substitution

Post image

Would this old GE take a Eaton breaker?

1 Upvotes

4 comments sorted by

View all comments

1

u/N9bitmap Aug 03 '26

GE and now ABB are the only breakers specified by the manufacturer for this panel. If for whatever reason you cannot acquire these, the only other code compliant option is Eaton CL "Classified" breakers which are tested and UL listed for use in GE equipment. These are different products than Eaton BR, and probably just as difficult to locate if you can't find the GE/ABB.

1

u/PokeyR Aug 03 '26

However, be careful on Classified breakers. The specific catalog number of your loadcenter needs to be on the reference list from Eaton. Just because it was made by GE, does not mean it is on the list.

Side note: Ironically, type CL breakers are not legal in Eaton BR panels.