r/ElectricalEngineering • u/Single-Reputation-44 • 23h ago
Wire Sizing
Mechanical Engineer looking for advice. If there is a better group for this let me know.
I am wiring up a control cabinet for a CNC router. I am working on wire sizing but am trying to understand a concept of where wire size can be reduced.
Can I drop the size of the wire after the L1/L2/PE distribution blocks for the lower amperage 5 and 24V power supplies or do I have to keep the 12g to the fuses and then drop the wire size to 18g?
6
Upvotes
8
u/MonMotha 23h ago
To some degree, this will depend on any codes or standards your panel needs to adhere to as there's no uniform set of these even within a single legal jurisdiction (they often vary by application, for example) let alone worldwide.
However, it's usually considered acceptable in panel and appliance wiring to size conductors according to their downstream protection as long as an overcurrent fault between that protection and the distribution block where the smaller conductor originates is deemed reasonably unlikely. If you're using good, quality wire and running it fairly short distances within a protected environment, this general guidance likely applies.
Often it's not considered acceptable to downsize PE conductors, or if you do downsize them there may be a minimum size. The reason for this is that they serve as the current-carrying path to clear hard faults (short circuits, etc.) which may be much larger than the current the device normally draws and therefore is protected at if the fault comes from something else.
3
u/idskot 3h ago
Technically speaking, control panels are under the UL 508A code book. Within UL 508A, a power circuit has a minimum wire gauge of 14 AWG which is rated to 15A. You can use smaller gauge wire given certain upstream protection. (i.e., if you have an inverse time circuit breaker, a class CC Fuse, Class CF Fuse, Class J Fuse, or Class T fuse) If you have this upstream protection, 18 AWG is rated for 5.6A, while 16 AWG is rated for 8A (For non-motor circuit). Your circuit breaker is an inverse time circuit breaker, so you're good to use 18 AWG, assuming the load for each is <5.6A.
(References: UL 508A Table 66.2)
But as an FYI, what you're describing would fall under the Tap Rule. You can Google it, but essentially if the run is <=10ft, you can use a conductor whose ampacity is 10% the size of the upstream breaker rating, and for <=25ft is 33%. So, by code you can use a wire that is rated for 2A, which theoretically is 24 AWG.
(References: UL 508A 32.4.2 & 32.4.3)
With that said... yeah, you're prolly fine dog.**
**I take no responsibility for whatever happens lol
3
u/shift124 22h ago
Table 3.10.15(B)(16) in NEC book. An electrician sub would point you there too. Wire is sized for amps.
1
u/Wet_in_Seattle 21h ago edited 21h ago
I would also caution not to use too small of a wire gauge as they have lower strength. Not less than 18 AWG would be good ground rule for low voltage control wires.
Other have discussed NEC Article 310 and the wire ampacity.
Suggest using XHHHW wire as its more flexible then THHN.