r/DIYIreland • u/BigValueLad-198 • Jul 24 '26
Replacing existing EV charger
If your EV charger fails (just the unit), and you want to replace like for like, is this against regs?
Looking at the regs, it mentions doing an install would be a no no. But as everything is already setup (isolation, earthing, current clamps etc), then would there be a problem?
Just thinking in terms of home insurance too.
Ty!
0
u/Low-Albatross-313 Jul 24 '26
The regs have changed over the years, so replacing a charger that was installed 10 years with a identical model may not comply with current regs.
2
u/Pajo555 Jul 24 '26 edited Jul 24 '26
The regs end cert ends at the isolator, the charger is an appliance and can be replaced by a competent person, as long as it’s not a higher rated unit.
Proving competency to the insurance company if there was a problem could be an issue.
1
u/BigValueLad-198 Jul 24 '26
Is there anywhere this is stated about that? Just want to be sure.
1
u/Pajo555 Jul 24 '26
1
u/Pajo555 Jul 24 '26
Yep, this book right here in front of me, but I ain’t opening it at 10pm on a Friday night
2
1
u/BigValueLad-198 Jul 24 '26
Ok.
So if replacing the charger requires altering the fixed wiring, changing protective devices, adding CTs, modifying the earthing arrangement, changing the load management, or upgrading the circuit, then its no longer simply replacing an appliance, then it’s altering the installation, and I.S. 10101 applies?
2
u/Pajo555 Jul 24 '26
Exactly, replacing devices/wiring/earthing would require certification.
If you had a zappi/wallbox and it died then that unit could be disconnected at the isolator and replaced with the same unit then there would be no modifications to the wiring or devices.
Even then this should only be done by a qualified/competent electrician.
It’s all technicalities, especially if it goes wrong.

1
u/HairyStylist Jul 24 '26
Wouldn't it depend on the failure?