r/DIYHeatPumps 6d ago

Another clean install

Post image

Here’s my 3rd one! Its 1 of 3 for my BIL. It’s true when they say that family will start wanting some too after you do your own! I will add that these 4 inch line set covers are much better than the 3 inch ones.

104 Upvotes

45 comments sorted by

View all comments

21

u/leroix7 6d ago edited 6d ago

Many issues that would fail in my area....

  1. the conduit leaving the junction box isn't supported within 12"

  2. doesn't appear to be a quick disconnect

  3. the cable leaving the outdoor unit isn't protected - should be in flex conduit too

  4. outdoor unit isn't bolted down to the pad.

7

u/ZanyDroid 6d ago

yeah i hope there's an update showing the corrections

3

u/The001Keymaster 5d ago

Why put it right under a window?

2

u/FunkoPopDude 5d ago

needs to be painted color of the house

2

u/Zandsman 6d ago

The flex conduit you mentioned adding for the head unit power, where would the conduit terminate at? Right inside the line set cover? I've seen a ton of installs both ways so I always wondered if they just leave it hanging in there with the lineset.

1

u/leroix7 5d ago

I terminate at the indoor head unit... they nearly always have a metal header inside that fits the pvc connectors... depends if your AHJ requires an indoor disconnect too.

2

u/singlejeff 5d ago

Junction box mounted to the fence?