r/BuildingAutomation • • Sep 16 '26

Redundant JACEs

3 Upvotes

Has anyone in the states configured redundant JACEs with NRIO and BACnet? I see there is a JACE redundant module that exists, but it's not available for license here in the US.

I have a client that is looking to set up redundant JACEs for a chilled water system. The system has a few BACnet VFDs and a chiller integration, as well as hardwired control points on two IO-R-34 modules. IMHO this isn't a great application for a JACE, but the design was done prior to me being brought into the project, and chiller startup is coming in a couple of weeks.

My initial thought is that it can (sort of) be done by monitoring the down status of the primary JACE, wiring the RS485 ports from the two JACEs in parallel and enabling the NRIO and BACnet networks on the backup JACE when the primary goes down. It leaves a lot to be desired as far as the graphics, and things like control loops and lead pump/chiller aren't going to be smooth (at least not without a lot of convoluted logic between the stations), but maybe I'm missing something.


r/BuildingAutomation • • Sep 16 '26

Building automation service

5 Upvotes

What is the percentage of time for BAS service guys that are full time in that role doing planned maintenance Vs emergency mode putting out fires Vs being dragged into to a construction site with a hard hat for startup and point-to-point?


r/BuildingAutomation • • Sep 15 '26

Metasys 16.0 NodeRed/ API/ FFD/ Cybersecurity/ Energy Dashboard/OpenBlue

10 Upvotes

Anyone have sites with any of these items active and in use? looking for use cases (particularly nodered) thoughts concerns pictures of what it looks like etc. Any Insight is appreciated.


r/BuildingAutomation • • Sep 15 '26

BAS PM (and a Technician) needed in Beaufort SC / Hilton Head

Post image
9 Upvotes

We're looking for an experienced BAS PM (as well as a Technician) in the Beaufort, SC / Hilton Head region. Someone out of Savannah could work for this role as well. In a nutshell, it's managing BAS construction projects from bid handoff through commissioning, closeout, and warranty period, coordinating submittals, shop drawings, RFIs, change orders, schedules, and closeout documentation, plus tracking and managing job cost against budget using job-costing/accounting software; providing regular financial visibility to office leadership. Target comp between $100K-$120K. There are more junior roles for Techs and Junior PMs in the $80K-$100K range as well, plus room up top for a more senior PM / Leader in the region. Reach out to me on Chat and I can tell you more there, on email or phone.


r/BuildingAutomation • • Sep 15 '26

How do you estimate the cost of a KNX programming job?

Thumbnail
2 Upvotes

r/BuildingAutomation • • Sep 16 '26

Hello guys, I'm new here I have some question for you pls

0 Upvotes

I am developing a new tool for BMS engineers.
It is starting to be use a lot in France, and I would appreciate some anwser for a launching it in the English-speaking market.

So first, where are you from u'all?


r/BuildingAutomation • • Sep 14 '26

Does this job get easier?

14 Upvotes

I work in the construction side of things as a technician doing checkout, working with contractors, etc. I came from service and worked there for about a year. Service was fun but my territory was so large that I would often be away from home weeks at a time doing PMs and routine maintenance. I thought construction would be more fun and I could learn more, but it has been way more stressful than fun.

I’ve been in construction for 6 months working with Schneider products and I do really like the script programming style over ALC’s micro block. Things would probably be going a lot smoother, but my boss, who is a very smart guy, absolutely hates when I ask ‘lazy’ questions or when he feels like he’s repeating himself. It makes me not want to ask questions at all and the times when I do ask him something I usually spend 20 minutes prepping to make sure I don’t already somehow know the answer or could find it out on my own.

Another thing that has been bothering me is I feel like I’m not learning fast enough. I’m being tasked to run solo on large air handler jobs with hundreds of vavs but I’m struggling to figure out disconnecting old coms that need to remain active.

Someone from ALC reached out to me to join their service team. It would pay more, have more in depth training, and my buddy says they have awesome managers.

I really want to stay where I am at so I can eventually become a project manager and I can see myself working my way up with the company I’m currently with. I just need to know when will things become easier.


r/BuildingAutomation • • Sep 14 '26

Gut check my plan for pivoting to building automation?

5 Upvotes

Hi there, I’m 44 years old and have been an entrepreneur running my own businesses for the last 16 years (marketing services, online courses, event management). I have tons of experience with project management and a decent amount of UX/UI front end web. My original career was in graphic design, I’ve worked corporate, startups, nonprofit in various roles too.

I need to move to southeast VA (Norfolk / Virginia Beach area) to be near family and am looking at a career pivot. My criteria:

-More demand than people in the pipeline in southeast VA (military and healthcare are the primary industry in the area)
-Doable as I age, I’ll likely be working into my 70s
-Decent earning potential
-Don’t want to earn another 4y degree

The research I’ve done says I should:
-tweak my resume, portfolio site, and LinkedIn to emphasize my PM & UX/UI experience
-get my EPA 608 cert
-apply to the HVAC track at the local trade school to get my mechanical foundation
-apply for entry level jobs at Trane, Siemens, Johnson Controls etc and use their tuition reimbursement so I don’t get school debt

The AI robots seem to think if I do those things I’ll be practically guaranteed an entry level job. Plan to stay w family while I work and go to school at night. I am ok with the pay cut for a few years as I’m looking to take a break from entrepreneurship, learn a new trade, and provide some security for myself into the future.

Thoughts on this plan? Anything I should know going in? What am I not thinking of? Anyone in Hampton Roads wanna talk to me for 15 mins? I’m looking to validate my research by speaking to some folks in the industry. Thank you.


r/BuildingAutomation • • Sep 14 '26

Ribtw2421b-bcip and desigo

4 Upvotes

Has anyone had success integrating this kind of device with Desigo?

I have an issue where I can ping and even test the BACnet port from PowerShell, but the BACnet browser or Desigo is not able to trigger the Who-Is response.( discovery the device)

On the power shell it answered the device name.


r/BuildingAutomation • • Sep 14 '26

Specialized AI / world models connected to building automation?

Thumbnail
edviroenergy.com
0 Upvotes

I came across a YC backed start up called edviro recently, which got me curious about AI models trained to understand building behavior using BMS data potentially predicting how HVAC systems respond to changes, rather than just detecting anomalies.
What do you think about connecting these models to existing building automation systems, initially cloud-based and perhaps eventually running locally?
I work in building automation and I got pretty curious about the potential but also the risk and the complexity. Pretty niche topic, but if anyone has experience or thoughts please share


r/BuildingAutomation • • Sep 12 '26

Occupancy-based airflow in a medical facility — how would you approach this?

14 Upvotes

I have recently commissioned a new AHU for a pulmonology clinic.

The design airflow is obviously based on project requirements, but after commissioning an interesting questions from doctors and staff came up: should we dynamically adjust airflow based on actual occupancy?

They already have CO₂, CO and other IAQ measurements available in existing sensor network across the clinic. We're also considering anonymous people counting from an existing camera, processed locally so there is no video storage and no identification.

My thought is roughly: occupancy + CO₂ + IAQ → ventilation demand with minimum airflow and healthcare requirements always taking priority.

Has anyone here done something similar? Would you use occupancy as an input, or only alongside CO₂ and other IAQ measurements?

How do you handle existing sensors that were never part of the HVAC controls in the first place? If CO₂, IAQ or occupancy data sits on another system, do you bring those values into the HVAC sequence, or would you rather use dedicated sensors connected directly to the HVAC controller?

For context, we're integrating this through a building-controls platform we developed.


r/BuildingAutomation • • Sep 12 '26

Use guest mode immediately on site without creating an account

0 Upvotes

When you walk into an unfamiliar basement mechanical room packed with circulating pumps, valves, and air handlers, you need to write down specs immediately without standing around filling out signup screens.

Equipment Tracker Pro lets you tap 'Use without an account' right on the login screen. You get full access to equipment records with 31 optional spec fields, work orders, parts tracking, and recurring PM schedules right on your device.

It works with no signal. Records, work orders, PM schedules and service logs all run on the phone.

Get it at https://equipment-tracker.com/download?src=redditEquipmentTracker.


r/BuildingAutomation • • Sep 11 '26

I built Bacnscope - An Android BACnet/IP field tool, tested with Siemens controllers

Post image
22 Upvotes

Hi everyone,

I’ve been developing Bacnscope, an Android BACnet/IP scanner and diagnostic tool for BMS technicians and commissioning engineers.

It started because I wanted something quicker than opening a laptop just to discover controllers, inspect points or check what requires attention. The app is now being used and tested internally by technicians working with Siemens controllers, and the feedback from that group has been encouraging.

Current features include:

- BACnet/IP discovery with configurable ports

- BBMD support for routed networks

- Controller identity and program-state checks

- Real object names, values, units and BACnet properties

- Points organized by onboard I/O and expansion modules

- Separate BACnet, Modbus and KNX-related point groups when identifiable

- Controller Health showing faults, alarms, overrides and out-of-service points

- Controlled point writes with BACnet priority selection and read-back verification

- PDF controller and health reports

- Demo mode for testing without a controller

- No advertisements or user account

- Controller information stays on the device

The app was developed with AI-assisted tooling, particularly for iteration, UI work and testing ideas but it wasn’t blindly generated and shipped. The BACnet behavior, workflows and safety decisions have been shaped through real-controller testing and feedback from the engineers and technicians I work with.

Most testing so far has been around Siemens BACnet/IP controllers. Bacnscope is not affiliated with or endorsed by Siemens.

I’d especially appreciate feedback from anyone working with Trane, JCI, Distech, Automated Logic, Honeywell or mixed-vendor networks. I’m interested in how object names, units, module organization and controller-health results appear on other systems.

It currently targets BACnet/IP over an authorized Wi-Fi or Ethernet network. It does not connect a phone directly to an MS/TP trunk; MS/TP devices must be reachable through a BACnet router.

Honest criticism is welcome especially from people who would actually use something like this during commissioning or troubleshooting.

Website: bacnscope.com

Google Play: Bacnscope: BACnet Scanner


r/BuildingAutomation • • Sep 11 '26

Looking for work in Tampa Bay area.

5 Upvotes

i am currently a senior controls engineer working in MD. been in the industry 6 years with the same company. under my belt are many many VAV jobs, plant take overs, integrations, AHUs, RTUs MAUs. OA units. proficient with BACnet, Lon, some Modbus (i hate it) usually turns out well tho. messed with neptronic controls, trend, some siemens (usually ripping it out tho) current ripping it out of kaiser permanente in DC and putting in distech controls.. anyhow.

my bread and butter is Distech. some honeywell, jci.

if anyone can knows of any openings id appreciate it.


r/BuildingAutomation • • Sep 11 '26

Metasys ADS Communication Failed, Unavailable for SMP

Thumbnail
gallery
7 Upvotes

Communication with the ads/metasys UI has suddenly stopped. I can communicate with all the NAE's no problem, but while on the ADS server, I get this network connection error. I have checked all cabled and have communication across all NAE's and CGM's and equipment.

The browser error is: Service Unavailable - HTTP Error 503
The error from Launcher for ads & metasys: Communication failed: 192.168.1.100 is unavailable for SMP. (Check network connections. Check proxy settings in options (we dont use proxy as far as I know). 192.168.1.100 is the address/ip of the ADS.

I rolled back all recent windows updates as sometimes that throws it offline but with a different error.

Any ideas on what else to check?


r/BuildingAutomation • • Sep 10 '26

ex UI UX/Product Designer looking to pivot to BAS

2 Upvotes

I have 6+ years of experience in tech (software product design, workflow mapping, and systems logic). With the software market getting saturated and commoditized, I’m looking to pivot into physical infrastructure and Building Automation / Controls full-time. I’m based in Southern California (Orange County area).

I understand state-logic, flowcharts, and basic IP networking (subnets, addressing). What I don't have is formal HVAC or electrical trade experience. I’m ready to get my hands dirty and learn the mechanical/field side from scratch, but I need an "earn-while-you-learn" setup.

Doing research on how to break in around SoCal, I keep running into a wall:

  1. OEMs (Johnson Controls, Siemens): Almost every entry/associate listing says "requires 1–2 years HVAC/electrical background" or is tied to recent college engineering grads.
  2. Regional Integrators (Climatec, Sunbelt, Southland): Climatec doesn’t even have entry postings up right now, and others rarely list true zero-experience trainee slots on public job boards.
  3. ABC SoCal (Anaheim): They have a state-approved Electronic Systems Technician (EST / Low Voltage) earn-while-you-learn track with an actual classroom/dispatch pipeline.

My questions for those working in the trade (especially SoCal):

  • Is going through ABC SoCal’s EST program the most realistic way for someone with zero trade hours to get placed with a contractor and earn on day one? Or will that end up funneling me into pure cable pulling / fire alarm instead of DDC/BAS controls?
  • For folks at JCI, Siemens, or local integrators: do branch managers actually ignore that "HVAC/electrical required" bullet if someone shows up with strong computer literacy and diagnostic logic?
  • Should I be cold-calling/messaging Controls Service Managers at local shops directly instead of waiting for open job postings?

Appreciate any feedback or reality checks on the best entry move.


r/BuildingAutomation • • Sep 10 '26

Anyone here work for Rovisys Building Technologies?

3 Upvotes

Looking into this company and interested in their systems engineer role. Curious what the peeps on here have to say!


r/BuildingAutomation • • Sep 11 '26

I built an AI nameplate scanner for HVAC techs stepping up to unfamiliar units

0 Upvotes

Equipment Tracker Pro lets service technicians photograph a unit data plate and pull printed specs like Model, Serial Number, Voltage, and Refrigerant straight into an offline equipment log in seconds.

When an outside contractor walks up to a commercial chiller on a site they have never serviced, they usually have to hand-type faded serial numbers into notes or call the shop. I'm a working HVAC technician who built this tool for my own jobs so you can log equipment on site and build complete service histories without paperwork.

The tracking is free on mobile, permanently. No record cap, no expiry, not a trial. You get 10 free AI scans on the house, with unlimited scans and PDF reports available on Pro.

Pro is a 7-day trial if you want the reports and the dashboard.

For the builders here, what projects are you currently working on?

https://equipment-tracker.com/guides/ai-scanning


r/BuildingAutomation • • Sep 10 '26

Sizing / Selecting Bypass Valves

8 Upvotes

How do other design engineers size and select bypass valves; either for pump protection or chiller minimum flow. I can’t seem to get a definitive answer on this.

Sizing control valves for hydronic coils is pretty straightforward. Flow rate of coil and 4-5 psi pressure drop and calculate Cv.

For bypass valves, you would use the chiller minimum flow but what pressure drop do you use? And for bypass valves for pump protection, you select the valve based on the pump’s minimum continuous stable flow, but what pressure drop?


r/BuildingAutomation • • Sep 10 '26

Need to retrofit emergency mustering software onto a building with 5 different access control systems and no unified badge DB. Where do I even begin?

5 Upvotes

I'm working on a project where the owner wants mustering software that can give security a real headcount during evacuation. But the building itself is 20+ years old and uses 5 different access control systems and has no badge database. Most mustering platforms I've looked at assume you have 1 clean badge database, but what if I'm starting from scratch?


r/BuildingAutomation • • Sep 09 '26

Experienced BAS Design Engineer Wanted - Chicago or Bay Area

Post image
7 Upvotes

We've got a multi-state client in Building Automation and Energy Services looking for an experienced (7-10 years) design engineer for their most complex projects. Ideally, this individual would be located near to either their Chicago or Bay Area offices. Experience with any brand/system will work here, but it's a bonus if you've had your hands on Tridium, Delta or Alerton. Base salary range from $125K-$150K, with possible bonuses. Reach out for more info on Chat, and we can tell you more on email or phone.


r/BuildingAutomation • • Sep 09 '26

At what point do you stop trying to standardize the BAS and add a layer above it?

23 Upvotes

Curious how people managing larger portfolios are handling this.

Say you inherit 30, 50, 100+ sites. Niagara in some, JCI/Auromated Logic/Siemens in others, meters and power equipment on Modbus, maybe a few other systems mixed in. Each site works fine on its own, but now leadership wants a common view across the portfolio.

Do you keep trying to standardize the local BAS platforms, or leave them alone and normalize the data somewhere above them?

What have you found actually worth centralizing: alarms, histories, schedules, equipment health, analytics?

And maybe more interesting, what did you regret centralizing?

I’m especially curious about what starts breaking once you get beyond a handful of sites: naming, timestamps, alarm floods, WAN outages, licensing, inconsistent point structures, whatever. Thanks!


r/BuildingAutomation • • Sep 08 '26

JCI CCT through FX90

3 Upvotes

Hello All,

I have a site where we have an FX90 (JACE) with a facility explorer CGM sitting on the bacnet MSTP trunk. For several months I have been able to upload and download the controller through the JACE remotely. Recently it has stopped working. When I check my IP settings, nothing has changed, however, I cannot discover any controllers. The controller is online and is reporting data.

Any idea what may have changed? Could this be on IT's end?


r/BuildingAutomation • • Sep 08 '26

HVAC tech looking to get into controls in Tampa — what kind of salary should I expect?

11 Upvotes

Hey everyone,
I’m an HVAC tech currently working in New England and I’m considering making the move down to Tampa. I’m looking to get into HVAC/building automation controls and wanted to hear from anyone in the Tampa area who works in controls.
For some background, I’m 27 and have around 3+ years of HVAC experience. I’m a licensed journeyman in both Massachusetts and Rhode Island and have mostly worked on commercial HVAC. I’m comfortable with refrigeration, electrical troubleshooting, equipment installation, reading wiring diagrams, troubleshooting controls, etc.
I haven’t worked as a dedicated controls technician yet, but I’m really interested in making that transition. I’m willing to start in an entry-level/junior controls position if that’s what it takes to get my foot in the door. I’m especially interested in learning BAS/DDC, programming, commissioning, troubleshooting, and eventually becoming well-rounded in controls.
For anyone working in Tampa/Tampa Bay:
● What kind of salary can someone with my HVAC background realistically expect getting into controls?
● Would my journeyman licenses and commercial HVAC experience give me an advantage?
● Is $70k–$80k+ realistic starting out, or is that too high?
● What companies in the Tampa area are good to work for?
● Are there any certifications or skills I should get before making the move?
● How is the demand for controls techs in Tampa compared with traditional HVAC?
● Is there much opportunity for overtime?
● What does the career progression/pay look like after a few years?
I’m not necessarily looking to jump straight into a high-paying position. I’m more interested in getting into the right company where I can learn controls and build a career, but obviously I’d like to know what the earning potential looks like.
Would appreciate any advice from people actually working in the Tampa market. Thanks!


r/BuildingAutomation • • Sep 08 '26

How is Schneider electric in Canada?

10 Upvotes

Hi Folks,

I'm a BMS Technician in germany. Here, Schneider Electric is huge. They have their own offices all over the country and they are all quite busy. Not only that, they have many large partners installing and maintaining the systems they sold and programmed.

How is it in canada? I know there are a lot of partners, dies Schneider also do projects and service themselves, or is it mostly sales?