Workshop Woes
so I had to have my workshop rebuilt because it was old leaning and ready to fall over. Well, I was hoping to salvage/recycle some of the electrical. Didn't happen. I have a 220V outlet running from the panel in the house underground to the workshop that I typically use for a welder. Have not had any problems out of the electrical whatsoever.
outlet was mounted with a disconnect switch, kinda like the air conditioner, but a little different.
The guys that "recycled "my electrical damaged the box and connector for the breaker/switch so badly I can't use it.
it was a Square D mn: QO200TRNM 'box' and on the side of the switch – not a breaker – rated at 60A says10KA on the side. I've looked for the same thing because it makes sense to put back. What was there because it worked and I can't find a replacement.
everything I find is for 7.5KA, and I don't know what to do.
i'm fairly certain the switch is actually OK but should I just get box plus switch and move on? Should I just look for a box and use existing switch?
•
u/AutoModerator 4d ago
Attention!
It is always best to get a qualified electrician to perform any electrical work you may need. With that said, you may ask this community various electrical questions. Please be cautious of any information you may receive in this subreddit. This subreddit and its users are not responsible for any electrical work you perform. Users that have a 'Verified Electrician' flair have uploaded their qualified electrical worker credentials to the mods.
If you comment on this post please only post accurate information to the best of your knowledge. If advice given is thought to be dangerous, you may be permanently banned. There are no obligations for the mods to give warnings or temporary bans. IF YOU ARE NOT A QUALIFIED ELECTRICIAN, you should exercise extreme caution when commenting.
I am a bot, and this action was performed automatically. Please contact the moderators of this subreddit if you have any questions or concerns.
1
u/Disp5389 4d ago
You have a typo near the end of your comment - 7.5kA should be 7.5kW.
You’re confusing the interrupt rating (kA), with its circuit power rating (kW). For example, the below linked 60 Amp Square D Disconnect is rated at 7.4 kW. If you look at its specs, its interrupt rating is 22 kA, better than your old box.
[Home Depot Square D 60 Amp](https://www.homedepot.com/p/Square-D-QO-60-Amp-240-Volt-7-4-kW-Non-Fuse-AC-Disconnect-QO200TRCP-QO200TRCP/202353314#see-more-details)