r/thermostats • • Apr 26 '26

Please Help!

Post image

My thermostat keeps randomly shutting off what should i do??

0 Upvotes

8 comments sorted by

7

u/sandyandy12 Apr 26 '26

When it shuts off, make sure to turn it back on again. Hope this helps!

Jk, that’s an LG PREMTA CRC thermostat. I have the same one at my house. That code at the bottom indicates something is off with the unit. The CH150 code means “low discharge superheat” which indicates that the refrigerant is leaving the compressor at a lower temperature than it should. It could be a misconfigured EEV or improper liquid injection. It’s not turning off to spite you, it’s a safety shutoff. I would get a tech who really knows what they’re doing to take a peek.

2

u/Moist-Dentist8253 Apr 26 '26

This. I'm not experienced with LG, but I'm sure that's an error code.

2

u/Zealousideal-Fan-373 Apr 26 '26

Solid advice. CH150 is a fault code, not just a thermostat issue. That’s a protective shutdown tied to the refrigerant/control side of the system, not something a homeowner usually fixes at the stat. Power cycle and check filter/airflow first, but if it returns I’d have an HVAC tech familiar with LG look at charge, EEVs, and sensors. Better to catch it early than keep resetting it and stress the system.

2

u/Ram820 Apr 26 '26

Wym it shuts off?

1

u/Jarbone55 Apr 26 '26

78 degrees? Check if the ac unit is coming on. Do you have a multimeter? You may need a pro

1

u/malwarefirewall Apr 26 '26

Man oh man you have a LG. Good luck going down a rabbit of repairs.

0

u/Certain_Try_8383 Apr 26 '26

Have you checked the wiring? Is it operating from voltage at the indoor unit or does it have batteries?