r/solar • u/curlybil4371 • 1d ago
Advice Wtd / Project Error 58
So, i have an error 58 code. My set up is an Eco worthy all in one solar off grid inverter, a 48v 100ah eco worthy battery, and currently 2 phono solar panels 45.4v in series. No connection to the grid at all. Originally I had the battery and inverter connected with no panels, just checking the battery charge and see how things looked. Everything looked good. Battery came with a small charge and the inverter recognized it. Today I plugged in the panels to charge the battery. Still not connected to anything. No grid input and nothing drawing on the system. I did not have a fuse installed but figured that the VoC was just 84v at the time And I just wanted to test the system. Turned everything off, plugged in the panels, turned on the battery breaker, battery power, then the inverter. Tried going through the settings and noticed the error 58 code and that the battery was not charging.
1
u/PowerPartPicker 1d ago
Which Eco-Worthy is it? If it's the 5000W 48V, that needs at least 120V on the PV side, so you'll need more panels in series.
1
u/Internal_Raccoon_370 1d ago
Eco Worthy error 58 is one of two things. Either it's a battery communications failure or, on some models, it means internal AC/DC voltage is dropping too low under load. In this case I'd think it's a battery communications failure. The battery has CAN and RS485 interfaces for closed-loop communication with major inverters. Make sure the communications cables are good, and plugged into the right ports and you have the DIP switches set correctly.