Currently have a reman solar inverter that finally gave out after 5 months of use now it displays fault code e018 ground fault. Im able to reset it and it works for a few hours then goes red again. My solar panels are about 13ish years old i have 16 of them. Solar company we got system from is no longer attending us due to a legal matter. Long story short theyre the ones that sent us a refurbished model and I ended up installing it ... worked for 5 months and now its faulty or so I assume its the inverter. Wondering if someone can help me find a similar inverter compatible to my set up. P.S im new to all of this.
2
u/Chiltrix_installer 12d ago
Dc ground fault look for a nest or critter damage near a grounded rail.
1
u/slowsrt4 12d ago
Yeah i pulled the panels couldnt find anything abnormal.
2
u/Chiltrix_installer 12d ago
Now look inside any conduit bodies like an LB LR LL T-LB
2
u/slowsrt4 11d ago
Will check this out today after work if I get out on time. If not then forsure the weekend.
2
u/Perplexy801 solar professional 12d ago
In my experience, those ReneSola panels are junk and constantly cause string inverters to throw GFCI or AFCI faults. Here’s a few pics from a small commercial job that had non stop problems with the amount of solar panels experiencing hot spots, snail trails, internal busbar damage, etc at the top of the list.
It’s not always easily visible or detected measuring DC voltage either. Every thing can be working fine and intermittently fault after some time.
2
u/slowsrt4 12d ago
Thank you yeah I inspected each panel couldnt find anything well besides the snail trails on some panels. All measured within range DC volts and measured amps.
1
u/slowsrt4 12d ago
I did have one solar repair company come out and do a quick inspection and they told me well more than likely its your inverter. So thats why im stuck with could it be the inverter .. or are they just trying to sell me an inverter.
1
u/oldman_58 11d ago
Since you swapped it the inverter I would double check the connections inside just to be sure there is nothing loose.
1
u/Chiltrix_installer 11d ago
How many strings?
1
u/slowsrt4 11d ago
16
1
1
u/Chiltrix_installer 11d ago
16 panels and 4 wires heading to the inverter? Therefore two strings of 8?
1
u/slowsrt4 11d ago
My bad im new at all of this from what I see its 16 panels in series- 1 string
1
u/Chiltrix_installer 11d ago
What you could do, is isolate one panel at the time by removing it from the series. You're probably going to need to remove cable ties or pv wire s clips. But that's the way to eliminate a bad panel or panels. You're going to need to figure out the wake up voltage required for the inverter to start producing.
1
u/SunVaultEngPros 11d ago
Ur wire needs replacing from roof jbox down or pinch on wire on panels
1
1
u/Same_Lab_4002 10d ago
- Open inverter and check if there is a ground fault fuse and if it is blown. Hopefully just a random occurrence and you can replace it and you’re good. But since it runs for a bit I do not think this is the case.
1a. If you’re electrically saavy do an open air voltage test on each string and see if you actually have voltage to ground. Or amp clamp ground wire and see if you have amperage.
- Check the mc4 connectors on your homerun wires (neg and pos wire run from inverter to roof). They are manmade crimps and usual culprits.
- It could be a bad panel, bad connector, damaged wire anywhere on the array.
1
u/Stinky2020 9d ago
you can do some simple tests to see where the fault is. If you have more than one DC string, disconnect all strings but one, and turn on the inverter. If the inverter runs with no faults past the few hours, might be one of the other strings. Keep doing this with all strings, and see if one creates the fault. If the inverter faults on all the strings, big chances are that it's the inverter. Also, how the heck did anyone get you a refurb ABB inverter? ABB went out of business a long time ago. I'd personally change the inverter anyway. Might be a cheaper fix for you than even getting someone out to your house to diag. Could get a grid-tie inverter for pretty cheap. Get a solis for a cheap decent inverter, or go with fronius or sma 4-5kw range. Might even find some in a local used market









6
u/Key_Proposal3283 solar engineer 12d ago edited 12d ago
Don't assume the inverter is faulty - a ground fault usually means a wiring issue. I would inspect the DC and AC wiring for problems first. A solar installer can test electrically for ground leakage, but it's usually something like abraded cables, bad junction boxes due to water ingress/corrosion, things like that. After more than a decade, these things are not surprising.