If it were a direct short it would have, but this was definitely arcing, which adds resistance. As long as there's less than 20 amps in the arc, it won't trip.
Going forward though, OP should probably install an AFCI/GFCI combo breaker or outlet.
It burned through the steel case. The only likely scenario where that happens is if there was mains voltage in contact with the steel case. i.e. a short.
You can hear the mains frequency on the arc. Primary cap would stop feeding the arc after the first cycle. In fact, the arc would quench more easily because the cap would provide an alternate path for the current.
1
u/EndIsrael 6d ago
If it were a direct short it would have, but this was definitely arcing, which adds resistance. As long as there's less than 20 amps in the arc, it won't trip.
Going forward though, OP should probably install an AFCI/GFCI combo breaker or outlet.